        Summary Cooling Design Table
        The Summary screen shows design cooling loads and flow rates for each 
 zone plus other related data.
         
        
            - Design Capacity, 
 shown in bold, is the maximum value of Total Cooling 
 Load and Sensible multiplied by the 
 Design margin to give the design cooling 
 capacity of the equipment. This value is written into the Cooling capacity 
 Model Data on the HVAC tab if the appropriate Plant 
 sizing Model Option is set.
- Design Flow Rate, 
 shown in bold, is the flow rate required to deliver the Sensible 
 cooling load using the Design supply temperature 
 and the zone air temperature at the time of the maximum load multiplied 
 by the Design margin.
- Total 
 Cooling Load is the total maximum Sensible 
 + Latent loads for the zone at the time 
 of maximum Sensible Cooling 
 load. If latent load is negative then it is ignored here and the Total 
 Cooling Load is the same as the Sensible load.
- Sensible is the 
 maximum Sensible Cooling 
 load for the zone in the Design day.
- Latent is the latent 
 load for the zone at the time of maximum Sensible load, calculated as 
 Total Cooling - Sensible 
 Cooling.
- Air Temperature is 
 the Air temperature in the zone at the time of maximum Sensible load.
- Humidity is the 
 humidity (%) in the zone at the time of maximum Sensible load.
- Time of Max Cooling 
 - the time at which the maximum sensible cooling occurs.
- Max Op Temp in Day is 
 the maximum operative temperature in the zone (using radiant fraction 
 = 0.5) over the design day including periods when the zone may be unconditioned.
- Floor area is the 
 floor area of the zone.
- Volume is the volume of the zone.
- Flow/Floor area 
 (MBH/ft2 in IP units) is the Design 
 Flow Rate divided by the Floor area 
 of the zone. It provides a useful check for the flow rates calculated.
 
        
             
        
         
        Use the Export command to export 
 this data in spreadsheet format.