Construction tab in model data under Airtightness header
Infiltration is included by default but you can switch infiltration off by unchecking the Model infiltration checkbox.
The infiltration rate (rate of entry of unintentional air from outside through cracks, holes and through the porosity of the fabric) is assumed to be constant throughout the simulation and can be set in one of 4 different units depending on the setting of the Infiltration units model option:
The air flow rate in m3/s at standard pressure is calculated from the ac/h data using:
m3/s = ac/h * ZoneVolume / 3600
where ZoneVolume is the total air volume of the space including the volume of floor and ceiling constructions and any raised floor and suspended ceiling voids (if selected in Separate constructions) and including half the volume of partition walls.
Note: this total zone volume value may be different from the value used for calculating air flow rates for natural ventilation and mechanical ventilation which have model options for excluding floor/ceiling constructions.
The ac/h at standard pressure is calculated from other units using formulae in EN12831 and the m3/s calculated using the above formula.
The schedule that modifies the maximum infiltration rate. The schedule should contain fractions between 0.0 and 1.0 and is used for Cooling design and Simulations but not for Heating design calculations which use a constant infiltration rate.
Note: Both the Infiltration rate and Schedule are only used in Simulations when the Scheduled natural ventilation model option is set. However this data is still used when Calculated natural ventilation is set for Cooling design calculations and Heating design calculations (Infiltration rate only). The captions for data used for design calculations only is displayed using a light grey background in the interface.