HVAC System Type
        HVAC tab in model 
 data 
        
         
        Compact HVAC systems are used when the HVAC 
 model option is set to Compact and is a powerful entry way into EnergyPlus 
 HVAC modelling allowing you to model HVAC systems in quite some detail 
 without the need to draw an air flow network and deal with the complexities 
 of control systems and node connections. You can model many common HVAC 
 systems including VAV with terminal reheat, VAV with PIU, Constant volume, 
 Fan coil units, Packaged DX units and Mechanical ventilation. 
         
        EnergyPlus simulations are carried out on the detailed HVAC component 
 models generated by DesignBuilder from the compact descriptions.
         
        When the HVAC model option is set to Compact, there are 5 HVAC system 
 types:
         
        
        Rules
        
            - Only one CAV, VAV or Unitary multizone system 
 can be defined per building.
 
            - If you select Unitary multizone, CAV or VAV at 
 zone level, then the same selection must be made at building level. 
 
            - You can enter Fan coil and Unitary single zone 
 systems in any zone without concern for the selection at building level.
 
            - Up to 400 zones can be modelled simultaneously 
 using Compact HVAC systems.  It 
 is possible to model more zones than this by making changes to the IDD file (contact 
 DesignBuilder or EnergyPlus Support desks for more information about this).
 
            - Pumps are modelled using typical default data.
 
            - Unitary multizone and Fan coil units cannot be 
 used in same building.
 
            - Fan coil units are incompatible with Calculated 
 natural ventilation.