This section documents the way the DesignBuilder model geometry you define is used in the calculations and visualisations. The description is based on the Model Geometry Example.dsb example building shown below. The file Model Geometry Example.dsb is supplied with DesignBuilder. The model consists of 4 blocks, each block containing a single zone, except the Ground floor block which is divided into equal sized North and South zones.
and Visualisation view:
See the Visualisation Limitations section for information on some minor differences in the rendered images and the model used in the calculations.
The model consists of:
1 x 10m x 10m Ground floor block partitioned into equal size North and South zones using partition of thickness 0.05m.
1 x 10m x 10m First floor block stacked on ground block.
1 x 10m x 5m Block with flat roof and external floor connects with the First floor block on the North side.
1 x 10m x 10m Roof block with 45° roof slope drawn in the vertical plane and extruded horizontally, i.e. it is not defined as a Pitched roof block form. The Roof block is stacked on top of the First floor block.
Above are external block dimensions.
Block wall thickness = 0.2m for all blocks.
30% Glazing ratio for all blocks, all glazing uses default facades (i.e. no windows or doors have been drawn).
Model uses default Zone volume calculation options - Internal floor constructions not subtracted from zone volume, External floor constructions not subtracted from zone volume and Ground floor construction is below ground and is not subtracted from zone volume.
When exported to 3-D DXF using the Whole model with details option and dimensioned the model looks like this:
The same model in 3-D view looks like this:
The ceiling / floor surface between First floor block - Zone 1 and Roof block - Zone 1 has area 9.6m x (9.6 - 2 x 0.2 / sin 45°) where the 0.2 / sin 45° term is the Roof block wall thickness (0.2m) adjusted to account for the roof slope (45°) as shown in the diagram below.
The dimension data for the zones, surfaces and openings used in the calculations can be seen in the Navigator and can also be obtained by exporting a csv report file.
The general principles used in DesignBuilder are:
The tables below list the most important geometric data and show how each item is calculated. Note that surfaces with glazing have area of glazing subtracted. The areas below are consistent with EnergyPlus and SBEM calculations.
| 
                     Zone Ground floor block - North  | 
                
                     
  | 
                
                     Calculation Note  | 
            
| 
                     Floor area (m2)  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
            
| 
                     Volume (m3)  | 
                
                     138.24  | 
                
                     46.08m2 x 3m (subtract volume of ground floor if Ground floor construction is below ground and is not subtracted from zone zolume model option set)  | 
            
| 
                     Surface  | 
                
                     Area (m2)  | 
                
                     Area Calculation Note  | 
                
                     Adjacency (Orientation / adjacent zone)  | 
            
| 
                     Ground floor  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
                
                     Ground  | 
            
| 
                     Ceiling  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
                
                     First floor block - Zone 1  | 
            
| 
                     Wall Outside  | 
                
                     10.08  | 
                
                     4.8m x 3m - glazing area on surface (2.88m x 1.5m)  | 
                
                     90  | 
            
| 
                     Glazing Outside  | 
                
                     4.32  | 
                
                     2.88m x 1.5m  | 
                
                     90  | 
            
| 
                     Wall Outside  | 
                
                     20.16  | 
                
                     9.6m x 3m - glazing area on surface (5.76m x 1.5m)  | 
                
                     0  | 
            
| 
                     Glazing Outside  | 
                
                     8.64  | 
                
                     5.76m x 1.5m  | 
                
                     0  | 
            
| 
                     Wall Outside  | 
                
                     10.08  | 
                
                     4.8m x 3m - glazing area on surface (2.88m x 1.5m)  | 
                
                     270  | 
            
| 
                     Glazing Outside  | 
                
                     4.32  | 
                
                     2.88m x 1.5m  | 
                
                     270  | 
            
| 
                     Partition  | 
                
                     28.8  | 
                
                     9.6m x 3m  | 
                
                     Ground floor block - South  | 
            
| 
                     Zone Ground floor block - South  | 
                
                     
  | 
                
                     Calculation Note  | 
            
| 
                     Floor area (m2)  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
            
| 
                     Volume (m3)  | 
                
                     138.24  | 
                
                     46.08m2 x 3m (subtract volume of ground floor if Ground floor construction is below ground and is not subtracted from zone volume model option set)  | 
            
| 
                     Surface  | 
                
                     Area (m2)  | 
                
                     Area Calculation Note  | 
                
                     Adjacency (Orientation / adjacent zone)  | 
            
| 
                     Ground floor  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
                
                     Ground  | 
            
| 
                     Ceiling  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
                
                     First floor block - Zone 1  | 
            
| 
                     Wall Outside  | 
                
                     10.08  | 
                
                     4.8m x 3m - glazing area on surface (2.88m x 1.5m)  | 
                
                     90  | 
            
| 
                     Glazing Outside  | 
                
                     4.32  | 
                
                     2.88m x 1.5m  | 
                
                     90  | 
            
| 
                     Wall Outside  | 
                
                     20.16  | 
                
                     9.6m x 3m - glazing area on surface (5.76m x 1.5m)  | 
                
                     180  | 
            
| 
                     Glazing Outside  | 
                
                     8.64  | 
                
                     5.76m x 1.5m  | 
                
                     180  | 
            
| 
                     Wall Outside  | 
                
                     10.08  | 
                
                     4.8m x 3m - glazing area on surface (2.88m x 1.5m)  | 
                
                     270  | 
            
| 
                     Glazing Outside  | 
                
                     4.32  | 
                
                     2.88m x 1.5m  | 
                
                     270  | 
            
| 
                     Partition  | 
                
                     28.8  | 
                
                     9.6m x 3m  | 
                
                     Ground floor block - North  | 
            
| 
                     First floor block - Zone 1  | 
                
                     
  | 
                
                     Calculation Note  | 
            
| 
                     Floor area (m2)  | 
                
                     92.16  | 
                
                     9.6m x 9.6m  | 
            
| 
                     Volume (m3)  | 
                
                     276.48  | 
                
                     92.16m2 x 3m (subtract volume of ground floor if Ground floor construction is below ground and is not subtracted from zone volume model option set)  | 
            
| 
                     Surface  | 
                
                     Area (m2)  | 
                
                     Area Calculation Note  | 
                
                     Adjacency (Orientation / adjacent zone)  | 
            
| 
                     Floor  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
                
                     Ground floor block - North  | 
            
| 
                     Floor  | 
                
                     46.08  | 
                
                     4.8m x 9.6m  | 
                
                     Ground floor block - South  | 
            
| 
                     Ceiling  | 
                
                     90.569  | 
                
                     9.434m x 9.6m (9.434m = 10 - 2 x 0.2 / sin 45°)  | 
                
                     Roof block - Zone 1  | 
            
| 
                     Wall Outside  | 
                
                     20.16  | 
                
                     9.6m x 3m - glazing area on surface (5.76m x 1.5m)  | 
                
                     90  | 
            
| 
                     Glazing Outside  | 
                
                     8.64  | 
                
                     5.76m x 1.5m  | 
                
                     90  | 
            
| 
                     Wall Outside  | 
                
                     20.16  | 
                
                     9.6m x 3m - glazing area on surface (5.76m x 1.5m)  | 
                
                     180  | 
            
| 
                     Glazing Outside  | 
                
                     8.64  | 
                
                     5.76m x 1.5m  | 
                
                     180  | 
            
| 
                     Wall Outside  | 
                
                     10.08  | 
                
                     9.6m x 3m - glazing area on surface (5.76m x 1.5m)  | 
                
                     270  | 
            
| 
                     Glazing Outside  | 
                
                     8.64  | 
                
                     5.76m x 1.5m  | 
                
                     270  | 
            
| 
                     0.201  | 
                
                     Necessary surround for interblock partition  | 
                
                     0  | 
            |
| 
                     28.649  | 
                
                     Interblock partition 9.6m x 3m - wall (with hole) (0.201m2)  | 
                
                     Block with flat roof and external floor - Zone 1  | 
            
| 
                     Block with flat roof and external floor - Zone 1  | 
                
                     
  | 
                
                     Calculation Note  | 
            
| 
                     Floor area (m2)  | 
                
                     44.16  | 
                
                     4.6m x 9.6m  | 
            
| 
                     Volume (m3)  | 
                
                     132.48  | 
                
                     44.16m2 x 3m (subtract volume of external floor if Internal and external floor construction is below ground and is not subtracted from zone volume model option set)  | 
            
| 
                     Surface  | 
                
                     Area (m2)  | 
                
                     Area Calculation Note  | 
                
                     Adjacency (Orientation / adjacent zone)  | 
            
| 
                     Floor  | 
                
                     44.16  | 
                
                     4.6m x 9.6m  | 
                
                     Outside  | 
            
| 
                     Flat roof  | 
                
                     44.16  | 
                
                     4.6m x 9.6m  | 
                
                     Outside  | 
            
| 
                     Wall Outside  | 
                
                     9.66  | 
                
                     4.6m x 3m - glazing area on surface (2.76m x 1.5m)  | 
                
                     90  | 
            
| 
                     Glazing Outside  | 
                
                     4.14  | 
                
                     2.76m x 1.5m  | 
                
                     90  | 
            
| 
                     Wall Outside  | 
                
                     20.16  | 
                
                     9.6m x 3m - glazing area on surface (5.76m x 1.5m)  | 
                
                     0  | 
            
| 
                     Glazing Outside  | 
                
                     8.64  | 
                
                     5.76m x 1.5m  | 
                
                     0  | 
            
| 
                     Wall Outside  | 
                
                     9.66  | 
                
                     4.6m x 3m - glazing area on surface (2.76m x 1.5m)  | 
                
                     270  | 
            
| 
                     Glazing Outside  | 
                
                     4.14  | 
                
                     2.76m x 1.5m  | 
                
                     270  | 
            
| 
                     0.201  | 
                
                     Necessary surround for interblock partition  | 
                
                     180  | 
            |
| 
                     28.649  | 
                
                     Interblock partition 9.6m x 3m - wall (with hole) (0.201m2)  | 
                
                     First floor block - Zone 1  | 
            
| 
                     Roof block - Zone 1  | 
                
                     
  | 
                
                     Calculation Note  | 
            
| 
                     Floor area (m2)  | 
                
                     90.569  | 
                
                     9.434m x 9.6m (9.434m = 10 - 2 x 0.2 / sin 45°)  | 
            
| 
                     Volume (m3)  | 
                
                     213.615  | 
                
                     90.569m2 x (5m - 0.2 / cos 45°) x 0.5  | 
            
| 
                     Surface  | 
                
                     Area (m2)  | 
                
                     Area Calculation Note  | 
                
                     Adjacency (Orientation / adjacent zone)  | 
            
| 
                     Floor  | 
                
                     90.569  | 
                
                     9.434m x 9.6m (9.434m = 10 - 2 x 0.2 / sin 45°)  | 
                
                     First floor block - Zone 1  | 
            
| 
                     Wall Outside  | 
                
                     15.576  | 
                
                     9.434m x (5m - 0.2 / cos 45°) x 0.5 - glazing area (6.676)  | 
                
                     90  | 
            
| 
                     Glazing Outside  | 
                
                     6.676  | 
                
                     4.45m x 1.5m  | 
                
                     90  | 
            
| 
                     Wall Outside  | 
                
                     15.576  | 
                
                     9.434m x (5m - 0.2 / cos 45°) x 0.5 - glazing area (6.676)  | 
                
                     270  | 
            
| 
                     Glazing Outside  | 
                
                     6.676  | 
                
                     4.45m x 1.5m  | 
                
                     270  | 
            
| 
                     Roof (slope 45° )  | 
                
                     64.042  | 
                
                     6.671m x 9.6m, 6.671 is the internal eaves to apex length = (5 - 0.2 / cos 45) / sin 45  | 
                
                     90  | 
            
| 
                     Roof (slope 45° )  | 
                
                     64.042  | 
                
                     6.671m x 9.6m, 6.671 is the internal eaves to apex length = (5 - 0.2 / cos 45) / sin 45  | 
                
                     270  |