Editing Air Loop

The air loop edit dialog allows you to control the way that the air system is sized and in particular in how the design supply and outside air flow rates as well as heating and cooling capacities are calculated.

 

See Generic Air Loop Tutorial

General

Name

This is the name of the loop. If the supplied loop name is found to already exist, the software will automatically append an integer to create a unique name.

Sizing

The rest of the Air loop dialog provides the sizing inputs needed to perform a central forced air system design air flow, heating capacity, and cooling capacity calculation for a system serving one or more zones. The information needed consists of the outside environmental conditions and the design supply air temperatures, outdoor air flow rate, and minimum system air flow ratio.

 

The outside conditions come from the design days in the input. A system sizing calculation is performed for the design day defined in the input file and the resulting maximum heating and cooling air flow rates and capacities are used in the component sizing calculations.

 

Supply air conditions are specified by inputting a supply air temperature for cooling, a supply air temperature for heating, and a preheat temperature. The system sizing calculation sums the zone design air flow rates to obtain a system supply air flow rate. The design conditions and the outdoor air flow rate are used to calculate a design mixed air temperature. The temperature plus the design supply air temperatures allows the calculation of system design heating and cooling capacities.

 

Note: Detailed HVAC autosizing calculations are not to be confused with Heating and Cooling design calculations, which use separate simpler data entry from the HVAC tab. No Detailed HVAC data is used for Heating and Cooling design calculations, which are based on the EnergyPlus Ideal loads system.

Design outdoor air flow rate

The design outdoor air flow rate (in m3/s or ft3/min). Generally this should be the minimum outdoor air flow. It is used for both heating and cooling design calculations. The assumption for cooling is that any outdoor air economizer will be closed. If Autosize is input the Design outdoor air flow rate will be taken from the sum of the zone outdoor air flow rates based on the Sizing option below.

 

Note that the Design supply air flow rate is defined in the AHU dialog contained within the Air loop.

Minimum system air flow ratio

This ratio is used in calculating the central system heating capacity and is only required when the Fan type of the attached AHU is 2-Variable volume. It should be set to the expected system flow rate when maximum heating demand occurs. Thus if the system is VAV with the zone VAV dampers held at minimum flow when there is a zone heating demand, this ratio should be set to the minimum flow ratio. If the zone VAV dampers are reverse action and can open to full flow to meet heating demand, this ratio should be set to 1.

 

The value entered must be between 0 and 1.

Sizing option

This value is read-only and set to as follows:

 

Type of load to size on

For CAV air loops you can define the way the central system supply air flow rate is sized. The choices are:

 

 

For VAV systems the Type of load to size on is always 1‑Sensible.

 

If you select the 2‑Ventilation requirement option in an air loop system where the AHU currently has recirculation set then DesignBuilder will offer to turn off recirculation in the AHU for you because when sizing on ventilation requirement the system will normally be full fresh air. You should therefore normally accept this offer unless you don't plan to save the changes you have made on this Air loop dialog and wish to maintain use of recirculation.

 

Note: For CAV air loops used to model a dedicated outdoor air system (DOAS), it is important to set the Type of load to size on to 2‑Ventilation requirement. This is true even if the air is being pre-heated and/or pre-cooled to temper it before delivery.

System outdoor air method

The method used to calculate the system minimum outdoor air flow. The two choices are:

 

 

1-Zone sum is the only option allowed in EnergyPlus v8. The VRP option causes EnergyPlus v8.0 to crash but this should be fixed in v8.1.

Zone maximum outdoor air fraction

For an air loop, when a zone requires outdoor air higher than the user specified Zone maximum outdoor air fraction, the zone supply air flow will be capped at the maximum value. This allows the system level outdoor air flow to be reduced while the total supply air flow increases. Valid values are from 0 to 1.0. Default is 1.0 which indicates zones can have 100% outdoor air maintaining backward compatibility. This inputs work for constant volume air systems, single and dual duct VAV systems.

Heating

Preheat design temperature

This is the design air temperature exiting the preheat coil (°C or °F).

Preheat design humidity ratio

This is the design humidity ratio exiting the preheat coil (in kg/kg).

Central heating design supply air temperature

This is the design supply air temperature for heating (°C or °F). This can be either the reset temperature for a single duct system or the actual hot duct supply air temperature for dual duct systems. It should be the temperature at the exit of the main heating coil.

 

The default value for newly added air loops is 16°C corresponding to a reheat-type system where the zone temperature control is provided through local reheat terminal units. Other system types without reheat will need a much higher value (typically 35-50°C).

100% Outdoor air in heating

This data is read-only and is set as follows:

 

Central heating design supply air humidity ratio

This is the design humidity ratio at the exit of the central heating coil (in kg/kg) . The default is 0.008.

Heating design air flow method

The input must be either:

 

 

The default method is 1-Design day, i.e., the program uses the calculated design values.

Heating design air flow rate

This is the design system heating air flow rate (m3/s or ft3/min). This input is an alternative to using the program calculated value. This input is used if Heating design air flow method is 2-Flow/System. This value will not be multiplied by any sizing factor or by zone multipliers. If using zone multipliers, this value must be large enough to serve the multiplied zones.

Cooling

Pre-cool design temperature

This is the design air temperature exiting the pre-cooling coil (°C or °F).

Pre-cool design humidity ratio

This is the design humidity ratio exiting the pre-cooling coil (kg/kg).

Central cooling design supply air temperature

This is the design supply air temperature for cooling (in °C or °F). This should be the temperature of the air exiting the central cooling coil.

 

This value should typically be lower than the Central heating design supply air temperature.

100% Outdoor air in cooling

This data is read-only and is set as follows:

 

Central cooling design supply air humidity ratio

This is the design humidity ratio at the exit of the central cooling coil (in kg/kg). The default is 0.008.

Cooling design air flow method

The input must be either:

 

 

The default method is 1-Design Day, i.e. the program uses the calculated design values.

Cooling design air flow rate

This is the design system cooling air flow rate (m3/s or ft3/min). This input is an alternative to using the program calculated value. This input is used if Cooling design air flow method is 2-Flow/System. This value will not be multiplied by any sizing factor or by zone multipliers. If using zone multipliers, this value must be large enough to serve the multiplied zones.

Availability schedule

Schedule values greater than zero (usually 1 is used) indicate that the system is on. Schedule values less than or equal to zero (usually 0 is used) denote that the system is off. This schedule overrides the air loop fan schedules for determining whether the fans are on.