PV thermal

Postby hawler1972 » Mon Apr 20, 2015 11:05 pm

hi , could you explain how to use the pv thermal instead normal pv in design builder , as it produce hot water and electricity ,

regards
mahmud
Andrew Bairstow
Site Admin
Posts: 504
Location: Birmingham, UK

Postby Andrew Bairstow » Mon Apr 27, 2015 10:09 am

Hi
SBEM does not permit the modelling of solar thermal sourced from PV. As the electricity generated by the PV is effectively subtracted from the electricity consumed in the building the final CO2 rate will be indicative of the whole output being used: though the individual service energies will not reflect the actual proportions of fossil fuels used for each. If hot water is otherwise supplied by a lower carbon fuel (eg gas) then the rating will be more optimistic. Please note if using sbem v5 (DB v4.2) you will almost certainly benefit from specifying using peak power rather than generic panel type.
Regards
Andrew
Andrew Bairstow
DesignBuilder Software
innervision
Posts: 1

PV-specify peak power

Postby innervision » Tue Sep 22, 2015 9:04 am

I am using DB 4.2.0.054 version.

For PV input, "specify peak power" is greyed out. I can only use "collector aperture area" and " panel type".

Not sure why DB does not allow specifying "peak power"?

Yanli