VRF Condenser Loop with Heat Injection

Help and discussion on using the Detailed HVAC option

Moderator: DesignBuilder Support

NirajP_GIW
Posts: 3

VRF Condenser Loop with Heat Injection

Postby NirajP_GIW » Wed May 17, 2017 8:16 am

Hi,

I am working on a project were a VRF system has been specified with a cooling condenser water loop system. I can model this easily enough in DesignBuilder (v5.03.007).

However, for winter operation, the cooling condenser water loop also includes a water heater for heat injection to prevent the loop temperature from dropping too low.

Is there a way to include heating for the condenser water loop? If not, is there an alternative way that the above system can be modelled e.g. with a gas fired basin heater?

Thanks!
Niraj
olafdybinski
Posts: 6

Re: VRF Condenser Loop with Heat Injection

Postby olafdybinski » Fri Dec 01, 2017 9:49 am

Hello,
did you find a solution for your problem? I am having quite similar problem at the moment.

Best regards,
Olaf
msweeney0312
Posts: 5

Re: VRF Condenser Loop with Heat Injection

Postby msweeney0312 » Fri Mar 09, 2018 3:53 pm

You can put a Loop-to-Loop Heat Exchanger on the Supply side of your Condenser Water Loop (parallel to the cooling tower), and connect the other side of the heat exchanger to a Hot Water Loop. Set the heat exchanger's operation to "Heating Setpoint Modulated", and place a setpoint manager equal to your heat injection setpoint directly at the outlet of the heat exchanger into the condenser loop.
WithWIthoutInjection.JPG
WithWIthoutInjection.JPG (115.25 KiB) Viewed 4096 times

Heat Injection Loop.JPG
Heat Injection Loop.JPG (77.08 KiB) Viewed 4096 times

Return to “EnergyPlus HVAC”

Who is online

Users browsing this forum: No registered users and 2 guests