Condenser Loop Setpoint Manager

Help and discussion on using the Detailed HVAC option

Moderator: DesignBuilder Support

MakiWatanabe
Posts: 2

Condenser Loop Setpoint Manager

Postby MakiWatanabe » Thu Aug 10, 2017 9:34 am

Is it possible to stop condenser loop when the cooling demand is zero?
I found in my model, cooling tower and condenser pump is working during cold season; especially pump (constant flow, intermittent) is working full load 24 hours 365 days (electric consumption is same as rated power x 24 x 365).
Condenser loop availability schedule did not stop cooling tower and pump. I guess I need to edit condenser loop setpoint manager.
Which option of the schedule and what set can I make them working only when the cooling demand occurs?

Thank you.
MakiWatanabe
Posts: 2

Re: Condenser Loop Setpoint Manager

Postby MakiWatanabe » Mon Aug 14, 2017 8:35 am

I tried editing schedules in vain. It seems Condenser Loop works throughout the year anyway.
However I am writing this to inform that I found a fault; Capacity control of the cooling tower was converted to Fluid bypass in the exported IDF file, even though I choose 1-Fan cycling in DesignBuilder.
That affect the annual electricity use by the Heat Rejection, because the Cooling tower fan drives all the time, full power.

Return to “EnergyPlus HVAC”

Who is online

Users browsing this forum: agrohimpsb and 2 guests