Results differ if applying window or hole with the same size

Forum for DesignBuilder CFD users to exchange views and ask each other questions

Moderator: DesignBuilder Support

hungdang
Posts: 3

Results differ if applying window or hole with the same size

Postby hungdang » Tue Jan 15, 2019 9:56 am

Hi,

I am studying on the internal wind environment for a simple terraced house. The room is my smallest unit for testing. I have a room 5m W x 5m D x 3m H. One door is in partition wall and one opening in exposed wall. I calculated airflow in and out through openings. I tried to use window or a hole of the same size in external wall Window opening was set 100% open, 24/7. The result between them is different. For use of window, many values of airflow through window are 0, especially at noon. For use of hole, all values are above 0. I need to these data for CFD calculation. So, i am confused about which opening element i should use window or replacement by a hole.
Can you help me?
Luis Sousa
Posts: 367
Location: Stroud

Re: Results differ if applying window or hole with the same size

Postby Luis Sousa » Fri Jan 18, 2019 3:33 pm

Hi,

Based on your description it looks like that the window is operating with temperature control that is the default control type for Calculated Natural Ventilation.
See Program Help http://www.designbuilder.co.uk/helpv6.0 ... atVent.htm

Holes in the other hand, are always considered open or with a constant control type.

BR,
Luis