Surface Convection
Construction
tab in model data under Construction header
You can select the inside and outside surface convection algorithms
in the Model data on the Construction tab under the Surface Convection
header. This
provides you with the option of making different selections in different
parts of the building.
Inside convection algorithm
You can select from 5 different EnergyPlus inside convection algorithms
for calculating the convection between internal zone surfaces and the
rest of the zone air in the simulation calculations:
- 1-Detailed - The detailed inside convection algorithm adjusts the convective heat transfer coefficient based on the surface orientation and the difference between the surface and zone air temperatures. The algorithm is taken directly from
Walton (1983). Walton derived his algorithm from the ASHRAE Handbook (2001), Table 5 on
p. 3.12, which gives equations for natural convection heat transfer coefficients in the turbulent
range for large, vertical plates and for large, horizontal plates facing upward when heated (or
downward when cooled). A note in the text also gives an approximation for large, horizontal
plates facing downward when heated (or upward when cooled) recommending that it should
be half of the facing upward value. Walton adds a curve fit as a function of the cosine of the
tilt angle to provide intermediate values between vertical and horizontal. The curve fit values
at the extremes match the ASHRAE values very well.
- 2-Simple - The simple convection model uses constant coefficients for different heat transfer
configurations, using the same criteria as the detailed model to determine reduced and
enhanced convection. The coefficients are also taken directly from Walton (1983). Walton
derived his coefficients from the surface conductances for ε=0.90 found in the ASHRAE
Handbook (1985) in Table 1 on p. 23.2. The radiative heat transfer component was estimated at 1.02 * 0.9 = 0.918 BTU/h-ft2-F and then subtracted off. Finally the coefficients
were converted to SI units to yield the values below.
For a vertical surface:
h = 3.076
For a horizontal surface with reduced convection:
h = 0.948
For a horizontal surface with enhanced convection:
h = 4.040
For a tilted surface with reduced convection:
h = 2.281
For a tilted surface with enhanced convection:
h = 3.870.
- 3-CIBSE - applies
constant heat transfer coefficient derived from traditional CIBSE values.
- 4-Ceiling diffuser
- a mixed and forced convection model for ceiling diffuser configurations.
The model correlates the heat transfer coefficient to the air change rate
for ceilings, walls and floors. The ceiling diffuser algorithm is based on empirical correlations developed by Fisher and
Pedersen (1997). The correlation was reformulated to use the room outlet temperature as
the reference temperature. The correlations are shown below.
For Floors:
h = 3.873 + 0.082 x ACH ^ 0.98, For ceilings: h = 2.234 + 4.099 x ACH ^ 0.503 and for Walls:
h = 1.208 + 1.012∗ACH ^ 0.604
- 5-Cavity - The Trombe wall algorithm is used to model convection in a "Trombe wall zone", i.e. the air
space between the storage wall surface and the exterior glazing. (See the later sections on
Passive and Active Trombe Walls below for more information about Trombe walls.) The
algorithm is identical to the convection model (based on ISO 15099) used in Window5 for
convection between glazing layers in multi-pane window systems. The use of the algorithm
for modelling an unvented Trombe wall has been validated against experimental data by Ellis
(2003).This algorithm gives the convection coefficients for air in a narrow vertical cavity that is
sealed and not ventilated. This applies both to the air gap in between panes of a window or
to the air gap between the Trombe wall glazing and the inner surface (often a selective
surface). These convection coefficients are really the only difference between a normal zone
and a Trombe zone.
The 5-Cavity Inside convection
algorithm is not available at the surface level.
Paraphrased note from EnergyPlus developers:
"The Trombe wall convection coefficients only make sense for a zone.
They are
specific coefficients calculated for a narrow enclosed space. The
two major walls of a Trombe wall zone are so close together that the convection
patterns for the two walls actually interact. If they are close enough
they can fight each other and totally stagnate the convection cell in
the space. This
is not free-boundary convection such as that found in a typical room.
Therefore,
it does not make sense to apply these coefficients to a single surface.
The algorithm
analyses the zone to figure out which are the two major surfaces and then
sets the coefficients on those surfaces. The
other minor surfaces receive negligible convection."
To avoid discontinuities in surface heat transfer rate calculations,
all correlations are extrapolated beyond the lower limit of the data set
(3 ACH) to a natural convection limit which is applied during the hours
when the system is off. These models are explained in greater detail in
the EnergyPlus Engineering Reference Document.
Outside convection algorithm
Substantial research has gone into the formulation of models for estimating the exterior
convection coefficient. Since the 1930's there have been many different methods published
for calculating this coefficient, with much disparity between them (Cole and Sturrock 1977;
Yazdanian and Klems 1994). You can select from 7 different outside convection algorithms:
- 1-Detailed - The Detailed, BLAST, and TARP convection models are very similar. In all three models,
convection is split into forced and natural components (Walton 1981). The forced convection component is based on a correlation by Sparrow, Ramsey, and Mass
(1979. The natural convection component is calculated in the same way as the Detailed
Inside convection algorithm (see above).
- 2-Simple - applies
heat transfer coefficients depending on the roughness and wind speed. This
is a combined heat transfer coefficient that includes radiation to sky,
ground, and air. The correlation is based on Figure 1, Page 25.1 (Thermal
and Water Vapor Transmission Data), 2001 ASHRAE Handbook of Fundamentals.
- 3-CIBSE - applies constant
heat transfer coefficients depending on orientation, derived from traditional
CIBSE values.
- 4-BLAST - Identical to the Detailed option
- 5-TARP - Identical to the Detailed option
- 6-DOE-2 - The DOE-2 convection model is a combination of the MoWiTT and BLAST Detailed
convection models (LBL 1994).
- 7-MoWiTT - The MoWiTT model is based on measurements taken at the Mobile Window Thermal Test
(MoWiTT) facility (Yazdanian and Klems 1994). The correlation applies to very smooth,
vertical surfaces (e.g. window glass) in low-rise buildings. The MoWiTT algorithm may not be appropriate for rough surfaces, high-rise surfaces, or surfaces
that employ movable insulation.
All
of the above algorithms are described fully in the EnergyPlus Engineering Reference.
When the surface is wet (i.e. it is raining and the surface is exposed
to wind) then the convection coefficient appears in results as a very
large number (1000) and the surface is exposed to the Outdoor Wet Bulb
Temperature rather than the Outdoor Dry Bulb Temperature.
Inside and Outside convection algorithm settings can be made
in various places.
- Model options dialog (Heating design, Cooling
design, Simulation tabs)
- Calculation options dialog (Heating design, Cooling
design, Simulation)
- Model data on Construction tab
You cannot make changes to individual surface convection settings where
the surface is an internal partition.
Note: the equivalent
inside and outside surface convection options in the Calculation and Model
options dialogs control building
default values (equivalent of making a setting in Model data at
building level) and changes at block, zone or surface levels in the Model
data will override these settings.