Open topic with navigation
        
        Vents and Holes
        Openings 
 tab in model data 
        
        Vents
        DesignBuilder vents are used for modelling airflow through openings 
 and are added to the model by navigating to the appropriate surface and 
 checking the Vents fitted option. This 
 adds a single vent under each of the windows (if the vent spacing is the 
 same as the window spacing). Alternatively, for more control over the 
 placement position of the vents, you can go to surface level and draw 
 the vents using the Draw vent command.  On 
 surfaces where custom openings have been defined, any changes to vent 
 layout model data on the Opening 
 tab is ignored.
         
        
         
        Note: if you 
 have drawn custom vents at the surface level then these will be used even 
 if the Vents fitted checkbox is not checked. 
 The Vents fitted checkbox only controls 
 the automatic generation of vents, not their use in the calculations.
         
        See also vent components for more 
 information.
        Holes
        Holes are modelled in a similar way to vents 
 with some exceptions:
         
        
            - Holes must be drawn at surface level
 
            - Airflow through holes is uncontrolled, i.e. the 
 airflow path is active all the time.
 
            - Drawing holes can be used as a way to merge 
 two zones when the Merge zones connected 
 by holes Model option is set.
 
            - Holes are used internally with DesignBuilder to 
 model the heat transfer and airflow through Virtual 
 partitions.
 
            - Discharge coefficient of 0.65 is used whereas 
 with vents the vent component defines the discharge coefficient.
 
        
        Vent modelling
        Calculated Natural Ventilation (Simulations 
 only)
         
        Each vent is modelled using:
         
        
            - An EnergyPlus 'Door'. The heat conduction through 
 the vent 'door' component is displayed in results as Internal 
 Natural vent and External Natural vent.
 
            - An EnergyPlus 'AIRFLOWNETWORK:MULTIZONE:COMPONENT 
 DETAILED OPENING' and other associated AIRFLOW components, providing a 
 controllable flow path. You can define Vent 
 operation.
 
        
         
        Scheduled Natural Ventilation (and Design 
 Calcs)
         
        Each vent is modelled using:
         
        
            - An EnergyPlus 'Door'. The heat conduction through 
 the vent 'door' component is displayed in results as Internal 
 Natural vent and External Natural vent.
 
            - Internal vents have an EnergyPlus 'Mixing' object 
 using parameters 
 set in the Model options dialog. 
 External vents .
 
        
        Hole modelling
        Calculated Natural Ventilation (Simulations 
 only)
         
        Each hole is modelled using a sub-surface and an airflow connection:
         
        
            - Sub-surface:
 
            
                - If using 1-Minimum 
 shadowing or 2-Full exterior solar 
 distribution the hole is represented using an EnergyPlus 'Door'. In this case the heat conduction through the 
 vent 'Door' component is displayed in results as Internal Natural vent 
 and External Natural vent.
 
                - If the 3-Full 
 interior and exterior solar distribution Model option is set then 
 the hole is modelled using a 'perfectly clear' window which transmits 
 solar radiation and visible light.
 
            
        
        
            - EnergyPlus 'AIRFLOWNETWORK:MULTIZONE:COMPONENT 
 DETAILED OPENING' and other associated AIRFLOW components, providing a 
 controllable flow path. You can define Vent 
 operation.
 
        
         
        Scheduled Natural Ventilation (and Design 
 Calcs)
         
        Each hole is modelled using a sub-surface and a 'mixing' flow:
         
        
            - Sub-surface:
 
            
                - If using 1-Minimum 
 shadowing or 2-Full exterior solar 
 distribution the hole is represented using an EnergyPlus 'Door'. In this case the heat conduction through the 
 vent 'Door' component is displayed in results as Internal Natural vent 
 and External Natural vent.
 
                - If the 3-Full 
 interior and exterior solar distribution Model option is set then 
 the hole is modelled using a 'perfectly clear' window which transmits 
 solar radiation and visible light.
 
            
            - Internal vents have an EnergyPlus 'Mixing' object 
 using parameters 
 set in the Model options dialog. 
 External vents.