Working with Large Models
It is possible to create very large complex building models using DesignBuilder
but you should consider what you're trying to achieve by your modelling
exercise before diving in and including every detail of the building design.
Otherwise you may find you have created a beautiful model which is impractical
to simulate because it takes too long or causes the simulation engine
to fail. You can should consider the following points.
EnergyPlus simulations are slowed down by:
- Lots of windows
- Lots of zones
- Lots of windows per zone
- Lots of surfaces
- VAV Compact HVAC descriptions
- Radiant heating systems
(Simple HVAC)
- Calculated natural ventilation using AIRNET
- Calculating solar
reflections
- Reading hourly or sub-hourly results for extended
simulation periods
- Not enough computer
memory (RAM)
- Lots of output
You can speed up simulations by using these techniques:
- Reduce the number of windows in the model by increasing
the Window spacing. Shading issues aside,
modelling a small number of large Windows has the same effect as a large
number of small Windows provided you get the frame area right.
- Use the Lump similar windows on surfaceoption to speed up simulations
with many similar windows per surface. Note that switching this option
on has no effect for zones using Daylight lighting control or if the Full
interior and exterior solar distribution option is selected.
- Only create zones to model areas of the building
with specific environmental conditions, and HVAC systems or internal gains
schedules. A
common mistake made by the 'beginners' is to model each room as a separate
zone. This
is generally not necessary because most rooms will have very similar operating
conditions. In
this case you may want to use one of the DesignBuilder Merging
features to reduce the number of zones.
- When you first create a building model you may
want to carry out simulations before partitioning the blocks into zones.
If your
unpartitioned blocks are very large there could be an enormous number
of windows in the single zone making up a block and this can slow down
EnergyPlus simulations especially if carrying out daylighting analysis.
In this
case you should try to reduce the number of windows in the model as recommended
above.
- Try to use the smallest number of blocks possible
to keep the number of surfaces down.
- Exclude
semi-exterior unconditioned zones from the model and replace them with
an R-Value.
- Use Simple,
(convective heating) HVAC descriptions.
- Use the Scheduled
Natural ventilation option.
- If you need to use Calculated
natural ventilation in your simulations then you should aim to minimise
the number of cracks and openings involved in the airflow calculations.
One way
to do this is to switch off infiltration calculations. Normally DesignBuilder
includes a single crack in each surface in the simulation to simulate
infiltration. If you have other openings such as vents, windows, doors
etc in a particular block/zone you can switch off infiltration. This approach
can be used in roof blocks or calculations such as cooling design where
infiltration is relatively insignificant.
- Switching off calculation of solar
reflections in the Model options dialog
- Restricting hourly and sub-hourly results to short
simulations for investigation of detailed building operation. You
should not attempt to generate hourly or sub-hourly results for a whole
year unless your model is very simple.
- If you are interested in analysing a single zone
within a much larger model, you could consider using the single
zone option to carry out simulations just on the zone, excluding consideration
of the rest of the building.
- Fit as much memory (RAM) to your computer as possible
(2-4 GB ideally). Paging memory to disk during simulations of large models
can cause EnergyPlus to grind to a halt.
- Only request the output you really need. This
will speed up simulation initialisation and reading of output (especially
hourly and sub-hourly) at the end. If you don't need surface data (Walls,
Windows etc. heat transfer) switch this off in the Output
Options tab of Simulation options dialog. If you are only looking
at hourly results switch off monthly and daily. You will get noticeably
faster initialisation.