This topic covers the Daylighting calculation options specific to the 2-LEED Simulation type.
Select from the supported versions of LEED:
1-LEED v2 - for NC 2.2 Credit EQ 8.1 (LEED v2)
2-LEED v3 - for Daylighting BD+C: New Construction v3
3-LEED v4 - for Daylighting BD+C: New Construction, Options 1 and 2
4-LEED v4.1 - for EQ Credit, Options 1 and 2
When the LEED version is set to one of 1-LEED v4 or 2-LEED v4.1, check this checkbox if you would like to run an annual sDA + ASE daylighting simulation suitable for assessing credits for Daylighting BD+C: New Construction, Option 1.
When the LEED version is set to one of 1-LEED v4 or 2-LEED v4.1, check this checkbox if you would like to run a point in time illuminance daylighting simulation suitable for assessing credits for Daylighting BD+C: New Construction, Option 2.
When running LEED annual daylight simulations, Dynamic blinds are simulated according to the requirements set out in LM-83-12.
For an explanation of the Dynamic shading method options, see the Dynamic shading method article under the General Simulation type.
By default the occupancy schedule used for each zone in the Annual simulations are based on the zone Occupancy schedule defined on the Activity tab, however you can override this to use the same occupancy schedule for each zone by selecting this option and selecting the schedule in the browse control below.
When the above Override zone occupancy schedule option is selected, you can select the occupancy schedule to be used to define when zones are occupied for all zones in the simulation. Values in the schedule greater than 0 indicate occupancy.
The default occupancy schedule provided by DesignBuilder does not include daylight saving time (DST). DST has to be added manually to the schedule. For example for the Northern Hemisphere you can use a schedule like the following:
Schedule:Compact,
8:00 - 18:00 Every day (DST Northern Hemisphere),
Fraction,
Through: 03/30,
For: AllDays,
Until: 08:00, 0,
Until: 18:00, 1,
Until: 24:00, 0,
Through: 10/26,
For: AllDays,
Until: 07:00, 0,
Until: 17:00, 1,
Until: 24:00, 0,
Through: 12/31,
For: AllDays,
Until: 08:00, 0,
Until: 18:00, 1,
Until: 24:00, 0;
There are 2 methods for generating the sky illuminance distribution when running the LEED v2 and v4 the Radiance calculations:
For LEED v4 and v4.1 point in time calculations, the 2-Perez all weather option is always used and this setting is not displayed.
There are 4 methods to choose from.
3-Direct horizontal irradiance for when measured (or calculated) direct horizontal and diffuse horizontal irradiance data is available. Such data can usually be found in EnergyPlus epw files in W/m2.
The sky properties must be set separately for morning and afternoon using data that depends on the Perez method selection .
Perez sky clearness (ε). Enter a value from 1.0 to 12.0.
Available only when using the 2-Perez all weather Sky method and the 1-Brightness and clearness Perez method
Perez sky brightness (Δ). Enter a value from 0.01 to 0.6.
Available only when using the 2-Perez all weather Sky method and the 1-Brightness and clearness Perez method
The direct normal solar broad spectrum irradiance (in W/m2 or W/ft2). This value can be found from the site level hourly weather data.
Available only when using the 2-Perez all weather Sky method and the 2-Direct normal irradiance Perez method.
The diffuse horizontal solar broad spectrum irradiance (in W/m2 or W/ft2). This value can be found from the site level hourly weather data.
Available only when using the 2-Perez all weather Sky method and the 2-Direct normal irradiance or 3-Direct horizontal irradiance Perez method have been selected.
The direct normal illuminance (visible spectrum) (in lux or fc).
Available only when using the 2-Perez all weather Sky method and the 4-Direct normal illuminance Perez method
The diffuse horizontal illuminance (visible spectrum) (in lux or fc).
Available only when using the 2-Perez all weather Sky method and the 4-Direct normal illuminance Perez method
An important part of the LEED v4 Option 2 daylight calculation is to set the sky conditions to be used in the simulations. This must be done using the 2-Perez all weather Sky method. The procedure required for this is described by USGBC:
Calculate illuminance intensity for sun (direct component) and sky (diffuse component) for clear-sky conditions as follows:
Method 1 using Direct horizontal irradiance
Based on LEED documentation:
- Obtain typical meteorological year data. Use local weather data or TMY weather data files for the nearest city.
- To calculate the illuminance intensity for sun (direct component) and sky (diffuse component) in a TMY2 or TMY 3 file, you can export the data into spreadsheet format.
- From the TMY, select the day within 15 days of September 21 that has the clearest sky condition (total sky cover at its lowest value) at 9 A.M.
- From the TMY, select the day within 15 days of March 21 that has the clearest sky condition at 9 A.M.
- Determine the direct horizontal irradiance (W/m2) values at 9 A.M. for the day selected in September and at 9 A.M. for the day selected in March. Average the two values and use the result in the 9 A.M. simulation as the direct horizontal irradiance input. If the file does not explicitly state direct horizontal irradiance, calculate it as follows:
Direct horizontal irradiance = Global horizontal irradiance – Diffuse horizontal irradiance- Determine the diffuse horizontal irradiance (W/m2) values at 9 A.M. for the day selected in September and at 9 A.M. for the day selected in March. Average the two values and use the result in the 9 A.M. simulation as the diffuse horizontal irradiance input.
- Repeat procedures 3–6 for 3 P.M.
- Choose the 2-Perez all weather Sky method (this is done behind the scenes for LEED v4 and v4.1).
- Choose the 3-Direct horizontal irradiance Perez method.
- Input the custom values for Direct horizontal irradiance and Diffuse horizontal irradiance in the Calculation options dialog and run the Radiance simulation.
Method 2 using Direct normal irradiance
Another (simpler) procedure to provide the sky condition data within DesignBuilder is as follows: