DesignBuilder provides a great deal of flexibility in the way that block and zone geometry is defined and passed through to the various calculations. There are various options including building blocks drawn using external measurements while providing correct internal zone geometry for floor area and zone volume calculations derived from actual surface thickness. It is also possible to use a simpler approach where the block and zone dimensions drawn are exactly the ones used in calculations and the thickness of the surfaces are not considered in the analysis.
Select the template which best fits the way you would like to define the building geometry. Templates provided include:
External measurements, internal zone geometry - blocks are defined using external measurements and surfaces dimensions, zone volume and floors areas are all derived from the inner zone geometry.
The usual inheritance mechanism applies so loading the required template at building level defines the geometry convention for the whole building. Settings can be made at building level only but Fixed surface thicknesses can be defined down to surface level and Void depths can be defined down to Zone level.
The Geometry convention template can also selected when creating a new building.
Tip: After making any changes to the model which could affect the geometry including construction type selection as well as the settings described on this page, you should manually refresh the Navigator by pressing the Refresh
Navigator toolbar icon. This will ensure that the Navigator is synchronised with the model.
This setting defines whether the geometric surface data used in the calculation (heat transfer etc) is based on the inner or outer zone volume dimensions. Options are:
Note 1: In cases where the 1-Inner volume option is selected and non-zero surface thickness settings are being used, any component block shading devices placed adjacent to the block at building level will not be exactly adjacent to the corresponding zone inner surfaces used in the simulations which are offset inwards from the block outer geometry. The resultant gap will allow solar radiation to pass into the windows which will not be apparent by looking at the model at building level or on the visualisation screen. You are therefore advised to avoid using the combination of 1-Inner volume geometry, non-zero surface thickness and external component blocks used as local shading devices. This issue does not arise with the local shading mechanism which ensures that overhangs, sidefins and louvre blades are offset with the window.
Note 2: In cases where the 1-Inner volume option is selected and non-zero surface thickness settings are being used, for some zone geometries, the inner volume cannot be generated and in this case the zone outer surfaces will be used instead. This issue is discussed in more detail below under Special Conditions.
This setting dictates whether internal or external measurements are used to calculate the zone volume is required to calculate air volumes etc.
Note: Unless otherwise specified by your regional modelling code, the 1-Inner volume setting should generally be used for calculating zone volume to allow it to account for the effects of surface thickness and any floor and ceiling voids included.
This setting dictates whether internal or external measurements are used to calculate the zone floor area. The options are:
The floor area calculated from the method selected here is used for:
Note: Unless otherwise specified by your regional modelling code, the 1-Inner volume setting should generally be used for calculating zone floor area.
Tip: For zones with walls that have a finite thickness, this floor area will not be the same as the total area of the floor surfaces listed in the Navigator, whose geometry is based on the Zone geometry and surface areas method.
This setting is used to specify whether or not the outside wall surface or inside wall surface is to used to calculate the available area for glazing. This option is only visible when the Zone geometry and surface areas option is set to 2-Outer. Options are:
Important Note: When the Window to wall ratio method is set to use the 2-Outer wall surface, rendered views on the Visualisation, Daylighting and CFD screens will default to a single skin display. Therefore all surface elements including walls, partitions, floors, ceilings and roofs are displayed without thickness, and floor and ceiling voids are not displayed. This allows full size windows to be rendered accurately. Special treatment is required for this option because windows can occupy the whole surface and in that case it wouldn’t be possible to show the extent of the windows together with the element thicknesses.
Also, because daylighting calculations use the same elements as seen on the Visualisation screen, the results will be based on the geometry seen there. So depending on the geometry of your model, the 2-Outer option may not be ideal if you are planning to use the model to run daylighting calculations.
Each surface can have its geometric thickness calculated from the construction selected but only when the checkbox for the associated surface type (list below) is unchecked. If the thickness is to be overridden then check the appropriate checkbox and enter the fixed surface thickness. Settings can be made from building level right down to surface level giving considerable flexibility over the model geometry.
In most cases you should simply select the Geometry convention template - you shouldn't normally need to override the surface thickness settings below.
When at zone level, the fixed surface thickness for internal surfaces are not displayed due to the ambiguity involved if the 2 zones involved in the connecting internal surface have different settings. This applies to Internal partitions, Internal floor, Semi-exposed wall, Semi-exposed floor and Semi-exposed ceiling data.
Note: The surface thickness does not affect the thermal properties of the wall/floor/roof etc (U-value, thermal mass etc). Surface thermal properties are based purely on the construction data specified for the surface.
If the external wall surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the wall thickness (in m or in).
If the below grade wall surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the wall thickness (in m or in).
If the partition surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the wall thickness (in m or in).
If the ground floor surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the floor thickness (in m or in).
Note: In most cases ground floor blocks are measured from ground level and the ground slab construction is not included in the volume of the building so this setting is normally overridden to be zero.
The basement ground floor is the construction used for underground ground floors (i.e. the floor is located at a height lower than z=0). If the basement ground floor surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the floor thickness (in m or in).
If the external floor surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the floor thickness (in m or in).
If the internal floor surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the floor thickness (in m or in).
If the semi-exposed wall surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the wall thickness (in m or in).
If the semi-exposed floor surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the floor thickness (in m or in).
If the semi-exposed ceiling surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the ceiling thickness (in m or in).
If the flat roof surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the flat roof thickness (in m or in).
If the pitched roof surface thickness is to be overridden (i.e. not derived from construction thickness) then check the checkbox and enter the pitched roof thickness (in m or in).
DesignBuilder CFD can include multiple zones in a single domain, but in this case it is important to ensure that all internal partitions and floors/ceilings separating zones in the domain have finite (non-zero) thickness. Any internal surfaces in the domain with zero thickness will be ignored in the analysis and so will not present a barrier to air flow.
When running parametric or optimisation studies in which wall or other surface thickness are changed as part of the parametric variations, there can be other significant knock-on impacts on the model geometry including varying floor area (and so internal gains, ventilation etc) and zone volume (and so ventilation and infiltration changes). To avoid running into these issues you can fix surface thickness for the relevant part of the model. For example if wall insulation thickness is being varied in a parametric analysis and you don't wish these changes to impact on zone floor area and volume then you could apply a constant External wall thickness.
Tip: the easiest way to avoid any such issues would be to use the "Simple" Geometry conventions template at the outset.
The depth of the ceiling void (in m or in). This is used, in addition to any surface thickness applied to the ceiling/roof surface to reduce the size of the zone inner volume and surfaces areas to account for the ceiling void.
When using the 1-Inner Zone geometry and surface areas option, ceiling voids will reduce the height of zone wall surfaces used in the simulation. Also when using the 1-Inner Zone volume calculation method option, ceiling voids will reduce the zone volume for air flow and heat exchange calculations.
Note: If the ceiling/roof construction already includes an air gap to define the ceiling void and its thickness is being used to define the inner volume then you should enter 0 here. Likewise, if the ceiling void is already modelled using its own zone then enter 0.
The depth of the floor void (in m or in). This is used, in addition to any surface thickness applied to the floor surface to reduce the size of the zone inner volume and surfaces areas to account for the floor void.
When using the 1-Inner Zone geometry and surface areas option, floor voids will reduce the height of the zone wall surfaces used in the simulation. Also when using the 1-Inner Zone volume calculation method option, floor voids will reduce the zone volume for air flow and heat exchange calculations.
Note: If the floor construction already includes an air gap for the floor void and its thickness is being used to define the inner volume then you should enter 0 here. Likewise, if the floor void is already modelled using its own zone then enter 0.
When writing out zone floor area and volume settings to the EnergyPlus input data, DesignBuilder uses the geometry convention settings described above. This ensures that the real usable floor area and actual zone air volume are used in the simulation. In many cases these values will be less than the values that EnergyPlus estimates when carrying out its input checking which is based only on the 2-D surfaces that make up the zone geometry. You will therefore often see warnings generated in the error file such as:
** Warning ** Entered Zone Volumes differ from calculated zone volume(s).
** ~~~ ** ...use Output:Diagnostics,DisplayExtraWarnings; to show more details on individual zones.
You can safely ignore these warnings.
When using 1-Inner Zone geometry and surface areas option, DesignBuilder creates an "inner volume" by moving all zone surfaces inwards using the construction thicknesses (or fixed thicknesses where specified). This process is called "deflation". In some cases, however the deflation process is not possible and the inner volume cannot be generated. The two main reasons for this failure are:

If the deflation process fails, the software uses an alternative mechanism in which the zone outer geometry is used for all zone thermal surfaces. Although DesignBuilder is unable to generate full inner zone geometry for these zones it can still calculate zone inner volumes and floor areas fairly accurately using a simpler algorithm based on the outer zone geometry and surface thicknesses.
Zone inner geometry is calculated zone by zone and so if the deflation process fails for 1 zone in a block, this should not affect the process in other zones in the block.
In cases where a surface is made up of more than one adjacency, each using a different construction, DesignBuilder must use an area-weighted average surface thickness. For example:
External measurements, perspective view
External measurements, section view
When modelling continuous glazing for curtain walls, atria, greenhouses etc. it is often necessary to model glazing joining at the corners. It is not possible for windows to literally meet in this way because EnergyPlus requires all openings (windows, doors etc) to be placed on a parent surface with at least a small gap between the opening and the parent surface edge. But by using a low value of wall surface thickness you can give the appearance of adjacent windows as shown below.
A small wall thickness, below, allows the glazing to cover most of the wall giving good results (below).
A larger wall thickness, below, requires more area to cater for the walls joining at the corners and the glazing does not meet 'round the corner' giving poor results (below).