Working with Large Models
It is possible to create very large, complex building models using DesignBuilder
but you should consider what you're trying to achieve by your modelling
exercise before diving in and including every detail of the building design.
Otherwise you may find you have created a beautiful model which is impractical
to simulate because it takes too long or causes the simulation engine
to fail. You can should consider the following points.
|
EnergyPlus simulations are slowed down by:
- Lots of windows
- Lots of zones
- Lots of windows per zone
- Lots of surfaces
- Radiant heating systems
- Calculated natural ventilation using the Airflow Network
- Calculating solar
reflections
- Reading hourly or sub-hourly results for extended
simulation periods
- Not enough computer
memory (RAM)
- Lots of output (quantity of data and number of reports)
- Lots of timesteps per hour
|
|
Note: You can speed up modelling, and in particular the drawing and deleting of partitions in large models, by switching off Automatic block zoning option.
You can speed up simulations by using these techniques:
- Reduce the number of windows in the model by increasing
the Window spacing. Shading issues aside,
modelling a small number of large Windows has the same effect as a large
number of small Windows provided you get the frame area right.
- Avoid unnecessary wiggles and indents in block perimeters and partitions - keep it as simple as possible. The larger the model the more important it is to follow this advice. Where an indent in the perimeter gives shading then you could instead model this using a single flat surface without indent and use local shading devices with sidefins to model local window shading.
- Use the Lump similar windows on surface option to speed up simulations
with many similar windows per surface. Note that switching this option
on has no effect for zones using Daylight lighting control or if the Full
interior and exterior solar distribution option is selected.
- Wherever possible lump similar adjacent zones together. Only create zones to model areas of the building
with specific environmental conditions, and HVAC systems or internal gains
schedules. A
common mistake made by the beginners is to model each room as a separate
zone. This
is often not necessary for building energy simulations because many rooms will have reasonably similar operating
conditions. In
this case you may want to use one of the DesignBuilder Merging
features to reduce the number of zones.
- If there are multiple identical zones then you can use the Zone multiplier to reduce the number of zones processed.
- When you first create a building model you may
want to carry out simulations before partitioning the blocks into zones.
If your
un-partitioned blocks are very large there could be an enormous number
of windows in the single zone making up a block and this can slow down
EnergyPlus simulations especially if carrying out daylighting analysis.
In this
case you should try to reduce the number of windows in the model as recommended
above.
- Try to use the smallest number of blocks possible
to keep the number of surfaces down.
- Exclude
semi-exterior unconditioned zones from the model and replace them with
an R-Value.
- Use Simple,
(convective heating) HVAC descriptions.
- Use the Scheduled
Natural ventilation option.
- If you need to use Calculated
natural ventilation in your simulations then you should aim to minimise
the number of cracks and openings involved in the airflow calculations.
One way
to do this is to switch off infiltration calculations. Normally DesignBuilder
includes a single crack in each surface in the simulation to simulate
infiltration. If you have other openings such as vents, windows, doors
etc in a particular block/zone you can switch off infiltration. This approach
can be used in roof blocks or calculations such as cooling design where
infiltration is relatively insignificant.
- Switching off calculation of solar
reflections in the Model options dialog
- Restricting hourly and sub-hourly results to short
simulations for investigation of detailed building operation. You
should not attempt to generate hourly or sub-hourly results for long periods (such as a whole
year) unless your model is simple.
- If you are interested in analysing a single zone
within a much larger model, you could consider using the single
zone option to carry out simulations just on the zone, excluding consideration
of the rest of the building.
- If you want to model a only a group of zones then you can exclude unnecessary zones by unchecking the Include zone model option.
- Fit as much memory (RAM) to your computer as possible
(2-4 GB ideally). Paging memory to disk during simulations of large models
can cause EnergyPlus to grind to a halt.
- Only request the output you really need. This
will speed up simulation initialisation and reading of output (especially
hourly and sub-hourly) at the end. If you are only looking
at hourly results then you can get noticeably
faster initialisation and simulations by switching off monthly and daily results. For example, simulation times for a test winter week simulation on a real model were:
- - With hourly, daily, monthly outputs: 39 min
- - Only hourly outputs: 14 min
- - Only hourly outputs and checking 'Internal surface as adiabatic': 12 min
- If you don't need surface data (Walls,
Windows etc. heat transfer) switch the Surface heat transfer incl solar output option off.
- Note that if you request large volumes of data this can result is a program crash when results are being loaded into DesignBuilder.
- It is sometimes possible to use less timesteps per hour to speed up simulations. Some models can give reliable results using 2 timesteps per hour, however when complex Compact HVAC systems are being modelled, 4, 6 or even 10 timesteps may be required. If you aren't sure, compare the hourly results you obtain when using a range of timesteps per hour values and choose the minimum value that gives results equivalent to the 6 or 10 timesteps case.
- If all else fails then you can model very large buildings by splitting them into smaller units and summing results outside DesignBuilder.