Chiller EIR

 

Chiller:Electric:EIR

 

Used in:

 

  • Chilled water loop, supply side

 

This chiller model is the empirical model used in the DOE-2.1 building energy simulation program. It uses performance information at reference conditions along with three curve fits for cooling capacity and efficiency to determine chiller operation at off-reference conditions. Chiller performance curves can be generated by fitting manufacturer’s catalog data or measured data. Performance curves for more than 300 chillers, including the default DOE-2.1E reciprocating and centrifugal chillers, are provided as templates for selection within the chiller dialog. This data comes from in the EnergyPlus Reference DataSets (Chillers.idf).

 

See the Chilled Water Loop and FCU Tutorial

Note: Chiller:Electric:EIR objects and their associated performance curve objects are developed using performance information for a specific chiller and should normally be used together for an EnergyPlus simulation. Changing the object input values, or swapping performance curves between chillers, should be done with caution.

General

Name

The auto-generated name of the chiller can be edited.

Chiller type

Select the type of the chiller from these options:

 

Chiller template

Use this browse option to select a chiller from the EnergyPlus chiller database whose performance data you wish to copy to your chiller.

Reference capacity

This numeric field contains the reference cooling capacity of the chiller (in W or Btu/h). This should be the capacity of the chiller at the reference temperatures and water flow rates defined below. Alternatively, this field can be autosized.

Reference COP

This numeric field contains the chiller’s coefficient of performance which is multiplied by the output of the chiller performance curves described below. This value should not include energy use due to pumps, evap-cooled or air-cooled condenser fans, or cooling tower fans. This COP should be at the reference temperatures and water flow rates defined below.

Compressor motor efficiency

This numeric input represents the fraction of compressor electrical energy consumption that must be rejected by the condenser. Enter a value of 1.0 when modelling hermetic chillers. This value must be between 0.0 and 1.0, with a default value of 1.0.

Chiller flow mode

This read-only data shows whether the chiller is modelled with constant or variable water flow through the evaporator. Valid settings are:

 

The flow mode can be changed by modifying the Plant loop flow type on the Chilled water plant loop dialog.

Sizing factor

The sizing factor is used when the chiller design inputs are autosized. In this case the autosizing results are multiplied by this additional sizing factor. The usual value to enter is 1.0.

 

The inputs that would be altered by the sizing factor are: Reference capacity, Reference chilled water flow rate and Reference condenser water flow rate.

 

The most common use of the sizing factor is for sizing chillers to meet only part of the design load while continuing to use the autosizing feature. For example when a set of chillers is chained together to supply chilled water to a plant loop, this sizing factor can be used to indicate the proportion of the load to be met by each chiller.

 

See also the section on Autosizing HVAC Components

Condenser

Condenser type

The condenser type determines what type of condenser will be included with this chiller. Valid condenser types are:

 

 

The default is 2-Water cooled which requires the full specification of the Condenser loop and its associated equipment. 1-Air cooled and 3-Evaporatively cooled do not require a Condenser loop to be specified.

Condenser fan power ratio

This data is used to model condenser fan power associated with air-cooled or evaporatively cooled condensers. Enter the ratio of the condenser fan power to the reference chiller cooling capacity in W/W.

 

During the simulation the condenser fan power for air-cooled or evaporatively cooled chillers is calculated as total chiller power consumption multiplied by this ratio.

Temperatures

Reference leaving chilled water temperature

This numeric field contains the chiller’s reference leaving chilled water temperature (in °C or °F). The default value is 6.67°C.

Reference entering condenser fluid temperature

This numeric field contains the chiller’s reference entering condenser fluid temperature (in °C or °F). The default value is 29.4°C. For water-cooled chillers this is the water temperature entering the condenser (e.g., leaving the cooling tower). For air- or evap-cooled condensers this is the entering outdoor air dry-bulb or wet-bulb temperature, respectively.

Leaving chilled water lower temperature limit

This numeric field contains the lower limit for the leaving chilled water temperature (in °C or °F). This temperature acts as a cut off for heat transfer in the evaporator, so that the fluid doesn’t get too cold. This input field is currently unused. The default value is 2˚C.

Flow rates

Reference chilled water flow rate

For a variable flow chiller this is the maximum water flow rate and for a constant flow chiller this is the operating water flow rate through the chiller’s evaporator. The units are (in m3/s or gal/min). This numeric input field must be greater than zero, or it can be autosized.

Reference condenser fluid flow rate

This numeric field contains the chiller’s operating condenser water flow rate (in m3/s or gal/min). This field can be autosized.

Performance Curves

Cooling capacity function of temperature curve

The name of a Bi-quadratic performance curve that parameterizes the variation of the cooling capacity as a function of the leaving chilled water temperature and the entering condenser fluid temperature. The output of this curve is multiplied by the reference capacity to give the cooling capacity at specific temperature operating conditions (i.e., at temperatures different from the reference temperatures). The curve should have a value of 1.0 at the reference temperatures and flow rates specified above. The bi-quadratic curve should be valid for the range of water temperatures anticipated for the simulation.

Electric input to cooling output ratio function of temperature curve

The name of a Bi-quadratic performance curve that parameterizes the variation of the energy input to cooling output ratio (EIR) as a function of the leaving chilled water temperature and the entering condenser fluid temperature. The EIR is the inverse of the COP. The output of this curve is multiplied by the reference EIR (inverse of the reference COP) to give the EIR at specific temperature operating conditions (i.e., at temperatures different from the reference temperatures). The curve should have a value of 1.0 at the reference temperatures and flow rates specified above. The bi-quadratic curve should be valid for the range of water temperatures anticipated for the simulation.

Electric input to cooling output ratio function of part load ratio curve

The name of a Quadratic performance curve that parameterizes the variation of the energy input ratio (EIR) as a function of the part-load ratio. The EIR is the inverse of the COP, and the part-load ratio is the actual cooling load divided by the chiller’s available cooling capacity. The output of this curve is multiplied by the reference EIR (inverse of the reference COP) and the Energy input to cooling output ratio function of temperature curve to give the EIR at the specific temperatures and part-load ratio at which the chiller is operating. This curve should have a value of 1.0 when the part-load ratio equals 1.0. The quadratic curve should be valid for the range of part-load ratios anticipated for the simulation.

Part Load Settings

Minimum part load ratio

This numeric field contains the chiller’s minimum part-load ratio. The expected range is between 0 and 1. Below this part-load ratio, the compressor cycles on and off to meet the cooling load. The Minimum part load ratio must be less than or equal to the Maximum part load ratio. The default value is 0.1.

 

Note: Setting the Minimum part load ratio to zero for air cooled chillers, will cause the condenser fan to run constantly even at zero load which is likely to lead to high chiller fan consumption. This happens because the condenser fan cannot cycle off even at zero chiller load.

Maximum part load ratio

This numeric field contains the chiller’s maximum part-load ratio. This value may exceed 1, but the normal range is between 0 and 1.0. The Maximum part load ratio must be greater than or equal to the Minimum part load ratio. The default value is 1.0.

Optimum part load ratio

This numeric field contains the chiller’s optimum part-load ratio. This is the part-load ratio at which the chiller performs at its maximum COP. The optimum part-load ratio must be greater than or equal to the Minimum part load ratio, and less than or equal to the Maximum part load ratio. The default value is 1.0.

Minimum unloading ratio

This numeric field contains the chiller’s minimum unloading ratio. The expected range is between 0 and 1. The minimum unloading ratio is where the chiller capacity can no longer be reduced by unloading and must be false loaded to meet smaller cooling loads. A typical false loading strategy is hot-gas bypass. The minimum unloading ratio must be greater than or equal to the Minimum part load ratio, and less than or equal to the Maximum part load ratio. The default value is 0.2.

 

Generic Chiller Outputs

Many output variable names are common across all chiller types. These generic chiller output names all begin with the word "Chiller". Certain chiller types have additional output variables which are specific to that type of chiller. Specific chiller output names begin with the chiller type, for example, "Gas Absorption Chiller Heating Energy [J]." Chiller energy use is added to the appropriate plant-level meters as a cooling end-use.

 

HVAC,Average,Chiller Electric Power [W]

HVAC,Sum,Chiller Electric Consumption [J]

Zone,Meter,Electricity:Plant [J]

Zone,Meter,Cooling:Electricity [J]

HVAC,Average,Chiller Evap Heat Trans Rate [W]

HVAC,Sum,Chiller Evap Heat Trans [J]

Zone,Meter,EnergyTransfer:Plant [J]

Zone,Meter,Chillers:EnergyTransfer [J]

HVAC,Average,Chiller Evap Water Inlet Temp [C]

HVAC,Average,Chiller Evap Water Outlet Temp [C]

HVAC,Average,Chiller Evap Water Mass Flow Rate [kg/s]

HVAC,Average,Chiller Cond Heat Trans Rate [W]

HVAC,Sum,Chiller Cond Heat Trans [J]

Zone,Meter,HeatRejection:EnergyTransfer [J]

HVAC,Average,Chiller COP [W/W]

 

The following output is applicable only for air-cooled or evap-cooled chillers:

 

HVAC,Average,Chiller Cond Air Inlet Temp [C]

 

The following outputs are applicable only for evap-cooled chillers:

 

HVAC,Average,Chiller Basin Heater Electric Power [W]

HVAC,Average,Chiller Basin Heater Electric Consumption [J]

 

The following three outputs are only available for water-cooled chillers:

 

HVAC,Average,Chiller Cond Water Inlet Temp [C]

HVAC,Average,Chiller Cond Water Outlet Temp [C]

HVAC,Average,Chiller Cond Water Mass Flow Rate [kg/s]

HVAC,Average,Chiller Shaft Power [W]

Chiller Electric Power [W]

Chiller Electric Consumption [J]

These outputs are the electric power input to the chiller. In the case of steam or fuel-powered chillers, this repesents the internal chiller pumps and other electric power consumption. Consumption is metered on Cooling:Electricity, Electricity:Plant, and Electricity:Facility.

Chiller Evap Heat Trans Rate [W]

Chiller Evap Heat Trans [J]

These outputs are the evaporator heat transfer which is the cooling delivered by the chiller. Chiller Evap Heat Trans is metered on Chillers:EnergyTransfer, EnergyTransfer:Plant, and EnergyTransfer:Facility.

Chiller Evap Water Inlet Temp [C]

Chiller Evap Water Outlet Temp [C]

Chiller Evap Water Mass Flow Rate [kg/s]

These outputs are the evaporator (chilled water) inlet and outlet temperatures and flow rate.

Chiller COP [W/W]

This output is the coefficient of performance for the chiller during cooling operation. It is calculated as the evaporator heat transfer rate (Chiller Evap Heat Trans Rate) divided by the “fuel” consumption rate by the chiller. For the constant COP and electric chillers, the “fuel” is electricity so the divisor is Chiller Electric Power [W]. For the absorption chiller, the “fuel” is steam so the divisor is Steam Consumption Rate [W].

 

For the engine driven chiller and combustion turbine chiller, the output variable is renamed as Chiller Fuel COP to clarify that the primary energy input to the chiller is a gaseous or liquid fuel (natural gas, diesel, gasoline, etc.). The divisor is the appropriate fuel consumption rate (Chiller [fuel type] Consumption Rate).

 

For the direct fired absorption chiller, this variable is renamed as Direct Fired Absorption Chiller Cooling Fuel COP and the divisor is Direct Fired Absorption Chiller Cooling Gas Consumption Rate.

 

Note that this variable is reported as zero when the chiller is not operating. When reported for frequencies longer than "detailed" (such as timestep, hourly, daily, monthly or environment), this output will only be meaningful when the chiller is operating for the entire reporting period. To determine an average COP for a longer time period, compute the COP based on total evaporator heat transfer divided by total electric or fuel input over the desired period.

Chiller Part-Load Ratio

This output is the operating part-load ratio of the indirect absorption chiller. This output may fall below the minimum part-load ratio specified in the input. For this case, the Chiller Cycling Fraction is used to further define the performance of the indirect absorption chiller.

Chiller Cycling Fraction

This output is the fraction of the timestep the indirect absorption chiller operates. When the chiller operates above the minimum part-load ratio, a chiller cycling fraction of 1 is reported. When the chiller operates below the minimum part-load ratio, the chiller cycling fraction reports the fraction of the timestep the indirect absorption chiller operates.

Chiller Cond Heat Trans Rate [W]

Chiller Cond Heat Trans [J]

These outputs are the condenser heat transfer which is the heat rejected from the chiller to either a condenser water loop or through an air-cooled condenser. Chiller Cond Heat Trans is metered on HeatRejection:EnergyTransfer, EnergyTransfer:Plant, and EnergyTransfer:Facility.

Chiller Cond Air Inlet Temp [C]

This output is the condenser (heat rejection) inlet temperature for air-cooled or evap-cooled chillers. For an air-cooled chiller, this output would be the dry-bulb temperature of the air entering the condenser coil. For an evap-cooled chiller, this output would be the wet-bulb temperature of the air entering the evaporatively-cooled condenser coil.

Chiller Basin Heater Electric Power [W]

Chiller Basin Heater Electric Consumption [J]

These outputs are the electric power input to the chiller’s basin heater (for evaporativelycooled condenser type). Consumption is metered on Chillers:Electricity, Electricity:Plant, and Electricity:Facility

Chiller Cond Water Inlet Temp [C]

Chiller Cond Water Outlet Temp [C]

Chiller Cond Water Mass Flow Rate [kg/s]

These outputs are the condenser (heat rejection) inlet and outlet temperatures and flow rate for water-cooled chillers.

Chiller Shaft Power [W]

Chiller Shaft Energy [J]

For engine-driven and turbine-driven chillers, these outputs are the shaft power produced by the prime mover and transferred to the chiller compressor.

Chiller Lube Heat Recovery Rate [W]

Chiller Lube Heat Recovery [J]

Chiller Jacket Heat Recovery Rate [W]

Chiller Jacket Heat Recovery [J]

Chiller Exhaust Heat Recovery Rate [W]

Chiller Exhaust Heat Recovery [J]

Chiller Total Heat Recovery Rate [W]

Chiller Total Heat Recovery [J]

For chillers with heat recovery, such as engine-driven chillers, these outputs are the components of recoverable energy available. For a given chiller type, one or more of the following components may be applicable: Lube (engine lubricant), Jacket (engine coolant), Exhaust (engine exhaust), and Total. Chiller Lube Heat Recovery, Chiller Jacket Heat Recovery, and Chiller Exhaust Heat Recovery are metered on HeatRecovery:EnergyTransfer, EnergyTransfer:Plant, and EnergyTransfer:Facility.

Chiller Exhaust Stack Temp [C]

This is the exhaust temperature leaving an engine chiller.

Chiller Heat Recovery Inlet Temp [C]

Chiller Heat Recovery Outlet Temp [C]

Chiller Heat Recovery Mass Flow Rate [kg/s]

These outputs are the heat recovery inlet and outlet temperatures and flow rate for chillers with heat recovery such as engine-driven and gas turbine chillers.

Chiller <FuelType> Consumption Rate [W]

Chiller <FuelType> Consumption [J]

Chiller <FuelType> Mass Flow Rate [kg/s]

Chiller Gas Mass Consumption [kg] (Gas Turbine Chiller only)

These outputs are the steam or fuel input for steam or fuel-fired chillers. Valid fuel types depend on the type of chiller. <FuelType> may be one of: Gas (natural gas), Steam, Propane, Diesel, Gasoline, FuelOil#1, and FuelOil#2. Consumption is metered on Cooling:<FuelType>, <FuelType>:Plant, and <FuelType>:Facility.

Chiller Electric EIR Outputs

These reports are available only for Electric EIR Chillers.

Chiller Condenser Fan Electric Power [W]

Chiller Condenser Fan Electric Consumption [J]

These outputs are for the electric power consumption of the chiller condenser fan and are applicable to air- or evaporatively-cooled chillers. This output is also added to a report meter with Resource Type = Electricity, End Use Key = Chillers, Group Key = Plant (Ref. Report Meter).

ChillerCapFTemp

This is the output of the curve object Cooling Capacity Function of Temperature Curve.

ChillerEIRFTemp

This is the output of the curve object Electric Input to Cooling Output Ratio Function of Temperature Curve.

ChillerEIRFPLR

This is the output of the curve object Electric Input to Cooling Output Ratio Function of Part Load Curve.

Chiller Part Load Ratio

This output is the ratio of the evaporator heat transfer rate plus the false load heat transfer rate (if applicable) to the available chiller capacity. This value is used to determine ChillerEIRFPLR.

Chiller Cycling Ratio

The cycling ratio is the amount of time the chiller operates during each simulation timestep. If the chiller part-load ratio falls below the minimum part-load ratio, the chiller cycles on and off to meet the cooling load.

Chiller False Load Heat Trans Rate

Chiller False Load Heat Trans

These outputs are the heat transfer rate and total heat transfer due to false loading of the chiller. When the chiller part-load ratio is below the minimum unloading ratio, the chiller false loads (e.g. hot-gas bypass) to further reduce capacity. The false load heat transfer report variable is not metered.