CFD Comfort Calculations

 

DesignBuilder CFD comfort calculations allow you to carry out a distributed analysis of the comfort conditions in the domain. The comfort calculations are carried out for each cell in the grid and include consideration of the local air temperature and velocity. Radiant temperatures of the surrounding surfaces are also considered. Note that solar radiation through windows or from zone equipment is not considered in DesignBuilder CFD.

 

After completing or pausing the CFD calculations the Update CFD comfort tool will become enabled. Clicking on this tool opens the comfort Calculation options dialog.

Comfort Calculation Options

Before the comfort calculations are run the comfort Calculation options dialog is displayed prompting for information on the values for metabolic rate, clothing and Relative humidity to be assumed in the comfort calculations (which use the Fanger comfort model).

Metabolic rate

Enter the metabolic rate to be used in the CFD comfort analysis. You should choose a value depending on the activity, age and sex of the occupants. If you are aiming to reproduce conditions in a previous EnergyPlus simulation then you should enter the same value used in that simulation. The default value for simulation is 0.90 met (the average of the recommended values for men and women). The default metabolic rate on this dialog is also 0.9.

Clothing level

Enter the clothing level for the CFD comfort calculations. The default is 1.0 which represents typical winter clothing.

 

If you are aiming to match comfort calculations with those in EnergyPlus you should ensure that you use the appropriate value. Note that EnergyPlus clothing levels are provided for summer and winter separately so you should make sure to choose the right value depending on the season for this CFD simulation.

Relative humidity

DesignBuilder CFD does not calculate relative humidity (RH) so this value must be defined manually by the user when calculating comfort. Again if you are aiming to reproduce the same values from a simulation you should copy the appropriate RH from the EnergyPlus results to this dialog. The default value is 50%.

Comfort results

After pressing OK on the Calculation options dialog, a progress bar will be displayed indicating that mean radiant temperature (MRT) calculations are in progress, followed by another progress bar for the comfort calculations themselves.

 

After the comfort calculations have completed additional comfort data will become available and corresponding comfort slice display variables are available on the Display options data panel:

 

 

 

You can find out more about Fanger comfort calculations in the EnergyPlus Thermal Comfort section.