Air Temperature Distribution - Dynamic Gradient
        HVAC tab 
 in model data 
        
         
        The Dynamic Gradient Air Distribution 
 model data allows you to model stratification within a zone by setting 
 up a temperature gradient which varies dynamically depending on:
         
        
            - Outside temperature.
 
            - Inside temperature.
 
            - Inside-outside temperature difference.
 
            - Heating load.
 
            - Cooling load.
 
        
        Gradient interpolation mode
        This field specifics how the program will vary between the two gradients. Select one of the following keywords to choose the simulation data used to scale:  ‘Outdoor Environment Drybulb Temperature’, ‘Zone Drybulb Temperature’, ‘Delta Outdoor and Zone Temperature’, ‘Sensible Cooling Load’, and ‘Sensible Heating Load’. These are explained in detail below. All of these options have several things in common. They are essentially hard-coded. There is no support for a general method. The interpolation scheme is based on some variable that might reasonably be expected to correlate with gradient changes. This variable’s current value is used to continually adjust the value of the vertical gradient for room air temperature.
         
        
            - 1-Outside temperature. This option directs the program to interpolate between upper and lower values of the vertical gradient based on the outdoor air temperature. If the outdoor temperature exceeds the upper limit set under the Upper Conditions header, then the gradient entered in the Upper Conditions > Temperature gradient  field is used. Similarly if the outdoor air temperature is below the value set in the Lower Conditions > Temperature field, then the gradient entered in the Lower Conditions > Temperature gradient  is used. For outdoor temperatures that lie between the upper and lower bounds, the gradient is determined by linear interpolation between the two.
 
            - 2-Inside temperature. This option directs the program to interpolate between upper and lower values of the vertical gradient based on the mean zone air temperature. If the mean zone air temperature exceeds the upper limit set under the Upper Conditions header, then the gradient entered in the Upper Conditions > Temperature gradient  field is used. Similarly if the mean zone air temperature is below the value set in theLower Conditions > Temperature field, then the gradient entered in the Lower Conditions > Temperature gradient  is used. For mean zone air temperatures that lie between the upper and lower bounds, the gradient is determined by linear interpolation between the two.
 
            - 3-Inside outside delta T.  This option directs the program to interpolate between upper and lower values of the vertical gradient based on the difference between the outdoor environment and the mean zone air temperature. If the temperature difference exceeds the upper limit set under the Upper Conditions header, then the gradient entered in the Upper Conditions > Temperature gradient  field is used. Similarly if the temperature difference is below the Lower Conditions > Temperature field, then the gradient entered in the Lower Conditions > Temperature gradient  is used. For temperature differences that lie between the upper and lower bounds, the gradient is determined by linear interpolation between the two.
 
            - 4-Sensible cooling load.  This option directs the program to interpolate between upper and lower values of the vertical gradient based on the sensible cooling load. If the cooling load exceeds the upper limit set under the Upper Conditions header, then the gradient entered in the Upper Conditions > Temperature gradient  field is used. Similarly if the cooling load is below the value set in the Lower Conditions > Heat rate field, then the gradient entered in the Lower Conditions > Temperature gradient  is used. For cooling loads that lie between the upper and lower bounds, the gradient is determined by linear interpolation between the two.
 
            -  5-Sensible heating load. This option directs the program to interpolate between upper and lower values of the vertical gradient based on the sensible heating load. If the heating load exceeds the upper limit set under the Upper Conditions header, then the gradient entered in the Upper Conditions > Temperature gradient  field is used. Similarly if the heating load is below the value set in the Lower Conditions > Heat rate field, then the gradient entered in the Lower Conditions > Temperature gradient  is used. For heating loads that lie between the upper and lower bounds, the gradient is determined by linear interpolation between the two.
 
        
        Upper Conditions
        Temperature
        This field is used to enter the upper bound on temperature values (in °C or °F). It is required for the interpolation modes based on temperature.
        Heat rate
        This field is used to enter the upper bound on heat rate values. It is required for the interpolation modes based on load. Both heating and cooling loads are entered as positive numbers (in W).
        Temperature gradient
        This field specifies the gradient, or slope, of temperature changes in the vertical direction (in ºC/m or °F/ft) when the selected temperature or heat load is at or above the upper condition.
        Lower Conditions
        Temperature
        This field is used to enter the lower bound on temperature values (in °C or °F). It is required for the interpolation modes based on temperature.
        Heat rate
        This field is used to enter the lower bound on heat rate values. It is required for the interpolation modes based on load. Both heating and cooling loads are entered as positive numbers (in W).
        Temperature gradient
        This field specifies the gradient, or slope, of temperature changes in the vertical direction (in ºC/m or °F/ft) when the selected temperature or heat load is at or below the lower condition.
        Operation.
        Operation schedule
        The operation schedule defines the times when air temperature distribution 
 is to be calculated. When the value of the schedule is 1, the distribution 
 calculations take place, when the value is 0, the zone air temperature 
 is fully mixed.
        Heights
        Thermostat  height
        Thermostat height specifies the distance above the floor where the thermostat 
 for HVAC control is situated. This height is used by the model to determine 
 the thermostat temperature relative to the mean air temperature by applying 
 the gradient.
        Return air height
        Return air height specifies the distance above the floor where the air 
 leaves the zone and returns to the air system. This height is used by 
 the model to determine the return air temperature relative to the mean 
 air temperature by applying the gradient.
        Range of applicability
        The air temperature distribution within the zone is used as follows:
         
        
            - To calculate boundary conditions for conduction 
 through surfaces (walls, roofs, glazing etc).
 
            - To include the effects of extracting relatively 
 warmer air at the ceiling level when using Compact HVAC.
 
            - To include the vertical position of the thermostat 
 sensor for HVAC control.
 
        
        How it works
        Changing the Distribution mode to 2-Dynamic gradient 
 reveals the air temperature distribution data. By default the Interpolation 
 mode is 2-Inside-outside DeltaT. This means 
 that the temperature gradient within the space is modelled as varying 
 according to the inside-outside temperature difference. The Upper conditions 
 define the most extreme temperature gradient, typically under design conditions. By default, the upper temperature difference is 10 °C 
 and the corresponding temperature gradient is 4 °C/m. This means that when 
 the temperature difference between inside and outside is 10 °C or more 
 the internal temperature gradient is 4 °C/m. The Lower conditions data 
 shows that when the temperature difference between inside and outside 
 is zero there is no temperature gradient, i.e. the air is fully mixed. 
 EnergyPlus calculates the temperature gradient for other inside-outside 
 temperature differences by linear interpolation. The calculation is similar for the other interpolation modes but is instead based on outside temperature, inside temperature, heating or cooling load.
        Limitations
        The air temperature distribution mechanism does not include:
         
        
            - The effects of extracting relatively warmer air 
 at the ceiling level when using Scheduled and Calculated natural ventilation.
 
            - The vertical position of the sensor for ventilation 
 control.