Plenums
        HVAC tab in model 
 data under Mechanical Ventilation 
 header - Compact HVAC
        
         
        Note: this topic relates to Compact HVAC. You can find out about plenums in Detailed HVAC in the Add Supply Plenum Add Return Plenum Tool topic.
         
        A plenum is an air compartment or chamber including uninhabited crawl 
 spaces, areas above ceilings or below a floor, including air spaces below 
 raised floors of computer/data processing centers, or attic spaces, to 
 which one or more ducts are connected and which forms part of either the 
 supply air, return air or exhaust air system, other than the occupied 
 space being conditioned.
         
        DesignBuilder Compact HVAC Unitary multizone, Unitary single zone, 
 VAV and CAV systems can have air supplied and returned via plenums. The system 
 supply and return plenums in the diagram below serve each of the 3 zones.
         
        
        
         
        There are 4 types of plenum:
         
        
            - System supply plenum 
 - a supply air plenum serving all zones 
 in 3-VAV and 2-Unitary multizone system. If any zone supply plenums have 
 been specified, the outlet from the system supply plenum will flow through 
 the zone supply plenum to the zone terminal unit. The system supply plenum 
 is defined at building level on the HVAC tab under the Plenums header and only one is allowed per simulation.
 
            - System return plenum 
 - return air plenums serving all zones 
 in 3-VAV and 2-Unitary multizone systems. If any zone return plenums have 
 been specified, the return air from the zone will flow through the zone 
 return plenum and then into the system return plenum. The system return 
 plenum is defined at building level on the HVAC tab under the Plenums header and only one is allowed per simulation.
 
            - Zone supply plenum 
 - a supply air plenum serving only this 
 zone in 3-VAV, 2-Unitary multizone and 1-Unitary single zone systems. 
 The plenum zone is added to the supply air path after the system splitter 
 or system-level supply plenum and before the zone terminal unit. The zone 
 supply plenum is defined at zone level on the HVAC tab under the Plenums header. A zone supply plenum can serve 
 only one zone.
 
            - Zone return plenum 
 - return air plenums serving only this 
 zone in 3-VAV, 2-Unitary multizone and 1-Unitary single zone systems. 
  The plenum 
 zone is added to the return air path immediately after the zone and before 
 the system mixer or system-level return plenum. The zone supply plenum 
 is defined at zone level on the HVAC tab under the Plenums header. A zone return plenum can serve only one zone.
 
        
         
        When specifying a system or zone supply or return plenum you should 
 enter a unique zone name. The 
 zone does not need to be in the same block. The zone name you enter is checked just prior to the simulation and not before so you should enter the names with care to avoid mistakes.
        Plenum modelling
        
            - Maximum of 1 system 
 supply plenum allowed per simulation
 
            - Maximum of 1 system 
 return plenum allowed per simulation
 
            - Each zone 
 plenum can only serve one zone
 
            - Set the Zone type 
 of any plenum zones to 4-Plenum. This makes the necessary changes (remaining 
 requirements and recommendations in bullet list)
 
            - Plenum zones cannot be controlled.  Use 
 the HVAC template <None> to switch 
 off heating, cooling and mechanical ventilation in all plenum zones.
 
            - Remember to ensure plenum zones have no internal 
 gains, occupancy, lighting etc.
 
            - We recommend using the 4-Ceiling diffuser interior convection 
 heat transfer coefficient for plenum zones to model the effect of fast 
 moving air on surface heat transfer.
 
            - You will probably find it easiest to use the Combined method 
 for Floor/slab/ceiling definition for models using plenums as each surface 
 element in the model has just a single construction and you don't have 
 the confusion of Model data referring to 'raised floors' and 'suspended 
 ceilings'.
 
            - The floor of a ceiling plenum is the ceiling of 
 the zone below so you will often define the plenum floor as 'Ceiling tiles' 
 construction or similar.
 
        
         
        If the building you are modelling has more than one plenum zone, each 
 serving multiple zones you should use zone 
 plenums. Use virtual partitions to partition the large plenum zones (which 
 in reality serve multiple zones) into multiple plenum zones, each serving 
 a single zone. See image below.
         
        
        
        Red lines show the 5 zones of the occupied space. Each zone has its 
 own return-air ceiling plenum.
         
        This technique is also illustrated in the example file supplied with 
 DesignBuilder Zone vs System Plenums Example.dsb.
         
        Note 1: when modelling plenums in DesignBuilder there is no need to add holes between the plenum and occupied space to represent supply diffusers or extracts. These are included in the model by EnergyPlus albeit as part of the system network.
        Note 2: it is 
 not possible in DesignBuilder v2 to use the suspended 
 ceiling/floor (as set on the Constructions tab when using Separate 
 constructions) as a plenum - the plenum must be a completely separate 
 zone.