The unitary air-to-air heat pump AHU incorporates an EnergyPlus unitary air-to-air heat pump component, an outdoor air system (see Air Handling Unit Outdoor Air System), optional night cycle operation, an optional heat recovery system (see Heat Recovery), optional pre-heat and pre-cool coils and an optional extract fan. The unitary air-to-air heat pump component itself comprises a supply fan, a DX cooling coil component, a DX heating coil component, and an electric supplementary heating coil component.
Tip: The Unitary Heat Cool AHU can be used to model ASHRAE 90.1 Appendix G System 4 PSZ-HP.
A detailed description of how the Unitary heat pump works is provided in the EnergyPlus Engineering Reference.
This is the name that you assign to the AHU which should be unique. If the supplied name is not unique, the software will automatically append a backslash and integer to ensure that there are no duplicate names.
This schedule contains information on the availability of the AHU for operation. A schedule value greater than 0 (usually 1 is used) indicates that the unit can be on during the hour. A value less than or equal to 0 (usually 0 is used) denotes that the unit must be off.
When this unit is unavailable (schedule values of 0) then all equipment contained within this AHU will also be switched off.
This is the air loop primary air design volumetric flow rate (in m3/s or ft3/min). This setting is auto-sizeable.
This setting defines the supply air flow rate leaving the heat pump (in m3/s or ft3/min) when the DX cooling coil is operating. Values must be greater than 0 or this field is auto-sizable.
This setting defines the supply air flow rate leaving the heat pump (in m3/s or ft3/min) when the DX heating coil and/or supplemental heater are operating. Values must be greater than 0 or this field is auto-sizable.
This setting defines the supply air flow rate leaving the heat pump (in m3/s or ft3/min) when neither cooling nor heating is required (i.e., DX coils and supplemental heater are off but the supply air fan operates). This setting is only used when the heat pump operating mode is specified as continuous fan operation (see Supply Air Fan Operating Mode Schedule). Values must be greater than or equal to zero, or this field is auto-sizable. If the heat pump operating mode is specified as continuous fan operation and this value is set to zero or this field is left blank, then the model assumes that the supply air flow rate when no cooling/heating is needed is equal to the supply air flow rate when the compressor was last operating (for cooling operation or heating operation).
Two fan types are available for selection in this AHU:
There are two options:
The supply air fan operating mode schedule can only be selected for On/Off fan types. The supply air fan operating mode may vary during the simulation based on time-of-day or with a change of season. Schedule values of 0 indicate that the unitary system supply air fan and the heating or cooling coil cycle on and off together to meet the heating or cooling load (sometimes referred to as an "AUTO" fan). Schedule values other than 0 denote that the supply fan runs continuously while the heating or cooling coil cycles to meet the load.
The default schedule is "Fan operation mode - Continuous" with a constant value of 1, i.e. that the supply fan runs continuously while the heating or cooling coil cycles to meet the load at all times. To obtain the AUTO fan configuration, select the "Fan operation mode - Cycling" schedule which has a constant value of 0.
An extract fan is included within all AHUs by default. This setting may be used to remove the extract fan from the AHU.
Note: This option is only available for Constant volume fan types. On/Off fans do not allow an extract fan to be included in the AHU and when this fan type is selected the Include extract fan check box will be disabled.
While the heat pump may be configured to serve multiple zones, system operation is controlled by a thermostat located in a single “control” zone. Click on the <Select zone> label and then click on the displayed ellipsis button to bring up the zone selector dialog. Select the zone supplied by the AHU where the thermostat controlling the heat pump is located.
There are two options for dehumidification control:
1‑None - meet sensible load only, no active de-humidification control;
2‑Cool Reheat - cool beyond the dry-bulb temperature set point as required to meet the high humidity setpoint.
Note: If 2‑Cool Reheat is used, a humidistat must be defined in one of the zones supplied by the AHU.
Tip: To provide humidification, a humidifier should be added to the AHU and a setpoint manager added downstream of the AHU with one of the "minimum humidity" control options.
If the heat pump’s DX heating coil output at full load is insufficient to meet the entire heating load, the part load ratio is set equal to 1.0 (compressor and fan are not cycling) and the remaining heating load is passed to the supplemental heating coil. If the outdoor air temperature is below the minimum outdoor air temperature for compressor operation, the compressor is turned off and the entire heating load is passed to the supplemental gas or electric heating coil.
This setting defines the maximum allowed supply air temperature exiting the heat pump supplemental heating coil.
This setting defines the outdoor air dry-bulb temperature above which the heat pump supplemental heating coil is disabled. The temperature for this input field must be less than or equal to 21°C.
See Night cycle description for Generic AHU
You can set up Mixed mode controls for the AHU to model optimal interaction between the natural ventilation system (Scheduled or Calculated) and the AHU.
Refer to the main HVAC tab Mixed Mode section for details on the available options.