Openings tab in model data under Vents
The operation of vents can be defined by entering timing data under Operation headers.
The control option allows you to define how internal vents behave in natural ventilation systems and whether they operate purely based on a schedule or, when using Calculated natural ventilation, whether they are linked to the main natural ventilation controllers defined on the HVAC tab. This data is not available for external vents. The options are:
For Calculated natural ventilation:
For Scheduled natural ventilation:
The way this data is used depends on the Natural ventilation model option set:
The ventilation rate through the vent is calculated based on the wind and stack pressure calculated at each time step in the simulation.
The Operation schedule is used to control timing of the vent opening availability. Note that the schedule should have values of 0 and 1 only and intermediate fractional values do not indicate partial opening.
External vent opening is not modelled explicitly with the Scheduled natural ventilation model data setting. Instead, the total natural ventilation flow rate and operation is defined for each zone on the HVAC tab. No operation data is entered on the Openings tab for external vents.
Internal vents are modelled using the EnergyPlus ZoneMixing object which mixes air between the two adjacent zones. DesignBuilder uses an approximate empirical relationship to calculate the mixing flow:
Flow (m3/s) = Door area (m2) * % area door opens * % time door is open * FAirflowRatePerOpeningArea
where FAirflowRatePerOpeningArea is a factor used to obtain the mixing flow from the opening area. The value of this factor can be defined on the Model options dialog on the Advanced tab under Natural ventilation. The default value is 0.1 m3/s-m2.
A schedule can be applied to control timing of the mixing flow.
Note: The Airflow through internal openings model option must be checked to obtain airflow through internal vents when using Scheduled natural ventilation.
The Operation schedule is used to control timing of the mixing flow. Note that the schedule should have values of 0 and 1 only and intermediate fractional values do not indicate partial opening.