Working with Large Models
        It is possible to create very large, complex building models using DesignBuilder 
 but you should consider what you're trying to achieve by your modelling 
 exercise before diving in and including every detail of the building design. 
 Otherwise you may find you have created a beautiful model which is impractical 
 to simulate because it takes too long or causes the simulation engine 
 to fail. You should consider the following points.
        
            
            
            
                
                    | 
                         EnergyPlus simulations are slowed down by: 
                          
                        
                            - Larger numbers of windows
 
                            - Zones with many windows and other surfaces (large number of surfaces / zone)
 
                            - Radiant heating systems
                            
 
                            - Calculated natural ventilation using the Airflow Network
 
                            - Calculating solar 
 reflections
 
                            - Reading hourly or sub-hourly results for extended 
 simulation periods
 
                            - Not enough computer 
 memory (RAM)
 
                            - Large volumes of output data
 
                            - Large values of timesteps per hour
 
                         
                     | 
                    
                         
                     | 
                
            
        
        
        
         
        Tip 1: You can speed up modelling, and in particular the drawing and deleting of partitions in large models, by switching off Automatic block zoning option. After having manually rezoned the block you can also save time when renaming the new zones by a) switching off the Double-click to navigate site hierarchy Program option and b) switching off the Automatically refresh site navigator lists Program option.
        Tip 2: Another way to speed up modelling in large models is to zoom into the area of the building or block where you wish to work. This eliminates consideration of objects that are not visible on the screen and allows the screen to refresh much more quickly. 
         
        You can speed up simulations by using these techniques:
         
        
            - Reduce the number of windows in the model by increasing 
 the Window spacing. Shading issues aside, 
 modelling a small number of large Windows has the same effect as a large 
 number of small Windows provided you get the frame area right.
 
            - Reduce the number of surfaces by avoiding unnecessary "wiggles" and indents in block perimeters and partitions - keep it as simple as possible. The larger the model the more important it is to follow this advice. Where an indent in the perimeter gives shading then you could instead model this using a single flat surface without indent and use local shading devices with sidefins to model local window shading.
 
            - Avoid very large zones with many surfaces and windows. Contrary to intuition, from the simulation time point of view, it is best to split such zones into more zones with fewer surfaces each.
 
            - Use the Lump similar windows on surface option to speed up simulations 
 with many similar windows per surface. Note that switching this option 
 on has no effect for zones using Daylight lighting control or if the Full 
 interior and exterior solar distribution option is selected.
 
            - Wherever possible lump similar adjacent zones together. Only create zones to model areas of the building 
 with specific environmental conditions, and HVAC systems or internal gains 
 schedules.  A 
 common mistake made by the beginners is to model each room as a separate 
 zone.  This 
 is often not necessary for building energy simulations because many rooms will have reasonably similar operating 
 conditions.  In 
 this case you can use one of the DesignBuilder Merging 
 features to reduce the number of zones.
 
            - If there are multiple identical zones then you can use the Zone multiplier to reduce the number of zones processed.
 
            - Try to use the smallest number of blocks possible 
 to avoid the need for block connection surfaces and keeping the number of surfaces down.
 
            - Use Simple HVAC descriptions.
 
            - Use the Scheduled 
 Natural ventilation option.
 
            - If you need to use Calculated 
 natural ventilation in your simulations then you should aim to minimise 
 the number of cracks and openings involved in the airflow calculations. 
  One way 
 to do this is to switch off infiltration calculations. Normally DesignBuilder 
 includes a single crack in each surface in the simulation to simulate 
 infiltration. If you have other openings such as vents, windows, doors 
 etc in a particular block/zone you can switch off infiltration. This approach 
 can be used in roof blocks or calculations such as cooling design in well sealed buildings where 
 infiltration is relatively insignificant.
 
            - Switching off calculation of solar 
 reflections in the Model options dialog
 
            - If you are interested in analysing a single zone 
 within a much larger model, you could consider using the single 
 zone option to carry out simulations just on the zone, excluding consideration 
 of the rest of the building. 
 
            - Alternatively if you want to model a only a group of zones then you can exclude unnecessary zones by unchecking the Include zone model option.
 
            - Fit as much memory (RAM) to your computer as possible 
 (8 GB or more ideally). Paging memory to disk during simulations of large models 
 can cause EnergyPlus to grind to a halt.
 
            - Only request the output you really need. This 
 will speed up simulation initialisation and reading of output (especially 
 hourly and sub-hourly) at the end. If you are only looking 
 at hourly results then you can get noticeably 
 faster initialisation and simulations by switching off monthly and daily results. For example, simulation times for a test winter week simulation on a real model were: 
- - With hourly, daily, monthly outputs: 39 min
 - - Only hourly outputs: 14 min
 - - Only hourly outputs and checking 'Internal surface as adiabatic': 12 min
 
 
            - If you don't need surface data (Walls, 
 Windows etc. heat transfer) switch the Surface heat transfer incl solar output option off.
 
            - Restricting hourly and sub-hourly results to short 
 simulations for investigation of detailed building operation. Note that if you request large volumes of hourly or sub-hourly data this can result is a program crash when results are being loaded into DesignBuilder. To avoid this you should switch off automatic loading of EnergyPlus results to DesignBuilder and view results instead using the Results Viewer.
 
            - It is sometimes possible to use less timesteps per hour to speed up simulations. Some models can give reliable results using 2 timesteps per hour, however when complex Detailed HVAC systems are being modelled, 6, 10 or more timesteps may be required. If you aren't sure, compare the hourly results you obtain when using a range of timesteps per hour values and choose the minimum value that gives results equivalent to the 10 timesteps case.
 
            - If all else fails then you can model very large buildings by splitting them into smaller units and summing results outside DesignBuilder.