Block and Zone Dimensions
        WARNING: THIS TOPIC REFERS TO V3 AND HAS NOT YET BEEN UPDATED
         
        See: Geometry Areas and Volumes
        Combined constructions
        The diagram below illustrates how blocks should be defined and how zone 
 volumes and surface dimensions are derived from the parent block when 
 using the default Combined 
 constructions model option. Note that there are 2 alternative dimensioning protocols:
         
        
            - UK NCM Convention which should always be used when using DesignBuilder for assessing buildings through the UK National Calculation Methodology, i.e. for Part-L and Section 6 Building Regulations checks and EPC/BER calculations.
 
            - Simulation and General Design Convention which should generally be used for all other applications where an NCM calculation is not required.
 
        
         
        
            
        
         
        The main differences between the 2 conventions are:
         
        
            - UK NCM Convention - For ground and intermediate floors, the block height is defined as "top of floor to top of floor" and for top floor blocks with a flat roof the block height is "top of floor to soffit/underside of roof slab". Details on defining building geometry for other less common geometries when using the NCM can be found in the Non Domestic EPC Conventions for England & Wales document. 
 
            - Simulation and General Design Convention - For ground floors the block height is "top of floor to bottom of floor". For intermediate floors, the block height is defined as "bottom of floor to bottom of floor" and for top floor blocks with a flat roof the block height is "bottom of floor to soffit/underside of roof slab".
 
        
        The important points to note for both conventions are:
         
        
            - The length/width dimensions of the block are measured 
 from the outside of external walls.
 
            - Zone height is always the same as block height, i.e. it is unaffected by block wall thickness or thickness of floor constructions.
 
            - Wall surfaces extend the full height of the block.
 
            - Flat roofs are placed on top of the block, so 
 when drawing a block with a flat roof you should exclude the roof 
 construction in the height.
 
            - External floors are placed under the block, so 
 when drawing a block with an external floor you should exclude the external floor construction thickness 
 in the height.
 
            - Zone surface dimensions (shown in green dotted 
 lines above) are measured from inner edges of outer walls and the centre 
 line of partitions. 
 
            - Floor surfaces extend horizontally to the inner 
 surface of external walls and to the centre line of partitions. See below 
 for more on zone/surface dimensions.
 
        
         
        
Show 
 diagram for Separate Constructions
        
        
            For Separate constructions the volume of the zone is calculated as the floor area x the block height. The volume of any floor and ceiling voids and associated constructions can be subtracted if the relevant model options are checked.
         
         
        The zone volume used in ventilation 
 calculations is the actual inside volume (shown in yellow in the diagram 
 above). These inside zone surface dimensions are used to define surface 
 heat transfer areas in simulations and other calculations.
        Zone perimeter (plan view)
         
        
        
         
        Other related information
        
            - See Combined 
 Constructions for information on the meaning of the Construction Model 
 data. 
 
            - Also see Constructions 
 for how to edit the construction configuration.
 
            - Block wall thickness for information on how zone inner volumes are created from external block dimensions
 
            - Construction and glazing model options for details of volume calculations with the options to include/exclude floor and ceiling volumes from the zone volume used in the energy calculations.
 
            - And the Model 
 Geometry Example section for a detailed worked example illustrating 
 how surface areas and volumes are calculated.
 
        
         
        
            
 The Creating a model Tutorial