Ground Heat Exchanger - Pond

The pond heat exchanger model represents a shallow pond with submerged hydronic tubes through which the heat transfer fluid is circulated. The model represents a "shallow" pond in that no attempt is made to model any stratification effects that may be present in deeper ponds.

 

This type of heat exchanger is intended to be connected to the supply side of a condenser loop, and can be used with any type of plant loop. The pond may be specified as the only heat exchanger on the condenser loop (as shown in top figure below) or it may be connected in parallel with other condenser loop heat exchangers (such as cooling towers, ground surface heat exchangers) as shown in the second figure below.

 

Pond heat exchanger as only heat exchanger on condenser loop

 

Pond heat exchanger with other heat exchangers on condenser loop

 

General

Name

This alpha field contains the identifying name for the outside pond heat exchanger.

Template

You can use this control to load data to the dialog from a pre-defined Ground heat exchanger template as a starting point for your particular pond component.

Type

DesignBuilder provides 3 different ground heat exchanger types:

 

 

The Type drop down list allows you to select the ground heat exchanger model to be used in this component.

Ground Heat Exchanger - Pond

Ground thermal conductivity

This numeric field contains the ground thermal conductivity (in W/mK or Btu-in/h-ft2-F).

Pond depth

This numeric field contains the pond depth (in m or ft).

Pond area

This numeric field contains the pond area (in m2 or ft2).

Number of tubing circuits

This numeric field contains the number of hydronic tubing circuits, total in parallel in this pond.

Length of each tubing circuit

This numeric field contains length (in m or ft) of each hydronic tubing circuit.

Hydronic tubing inside diameter

This numeric field contains the hydronic tubing inside diameter (in m or in).

Hydronic tubing outside diameter

This numeric field contains the hydronic tubing outside diameter (in m or in).

Hydronic tubing thermal conductivity

This numeric field contains the hydronic tubing thermal conductivity (in W/mK or Btu-in/h-ft2-F).