Condensation Analysis

Condensation analysis tab on Constructions Dialog.

 

DesignBuilder Condensation Analysis allows you to generate reports on the occurrence of interstitial and surface condensation based on the ISO 13788 standard.

 

The analysis is accessed from the Condensation analysis tab on the Constructions dialog. Controls are provided under the Options header to control the outputs generated and there are also tools to allow you to set internal and external boundary conditions for the condensation calculations.

 

The moisture vapour resistance properties for each material used in the construction layers must be entered on the materials dialog for accurate condensation analysis results.

Options

Data under the Options header allows you to set various calculation and display options for the condensation analysis.

Show Glaser diagram

Check this option if you would like to view a Glaser diagram showing a graphical section through the construction with temperature, partial vapour pressure and saturated vapour pressure data plotted.

Month

When viewing a Glaser diagram select the month from the drop list. The default option is 13-Worst case month where DesignBuilder displays results for the month with the worst case of moisture build up.

Show interstitial condensation details

If you would like to view details of the monthly and cumulative condensation build up for each interface with condensation then check this option. In this case, if condensation is present you will see output similar to:

 

Interface

If you requested interstitial condensation details then you should enter the interface number here. The definition of each interface with condensation is given under the Condensation Interfaces heading in the report.

Surface condensation calculation

To see surface condensation details check this box. In this case you should enter further details to define the boundary conditions as explained below.

Environment source

Select from:

 

 

In all cases monthly external conditions are defined in the Boundary data.

Fixed internal air temperature

Enter the constant internal air temperature for the Surface condensation calculation.

Fixed internal RH

Enter the constant internal relative humidity for the Surface condensation calculation.

Humidity class

Enter the humidity class for the Surface condensation calculation. The allowed classes are as follows:

 

Humidity Class Building Type
1 Storage areas
2 Offices, shops
3 Dwellings with low occupancy
4 Dwellings with high occupancy, sport halls, kitchens, canteens; buildings heated with un-flued gas heaters
5 Special buildings

Show surface condensation details

Check the Show surface condensation details checkbox to display a table similar to the one below in the report.

 

 

Ext Temp

Ext RH (%)

Int Temp

Int RH (%)

Min Temp Factor

Min Tsi

Tsi

Jan

3.9

85

20.0

50

0.633

14.1

19.3

Feb

3.9

82

20.0

50

0.633

14.1

19.3

Mar

5.7

79

20.0

50

0.586

14.1

19.3

Apr

8.0

75

20.0

50

0.507

14.1

19.5

May

11.3

73

20.0

50

0.320

14.1

19.6

Jun

14.2

75

20.0

50

-0.020

14.1

19.7

Jul

15.8

75

20.0

50

-0.408

14.1

19.8

Aug

15.7

77

20.0

50

-0.375

14.1

19.8

Sep

13.5

80

20.0

50

0.090

14.1

19.7

Oct

10.6

83

20.0

50

0.371

14.1

19.6

Nov

6.4

85

20.0

50

0.565

14.1

19.4

Dec

4.6

86

20.0

50

0.616

14.1

19.3

Example Output

An example report generated by the Condensation analysis tool is shown below.

Condensation Analysis Report

Interstitial Condensation

Interstitial condensation occurs at one or more interfaces but all condensate is predicted to evaporate during the summer months.

The risk of degradation of building materials and deterioration of thermal performance as a consequence of the calculated maximum amount of moisture shall be considered according to regulatory requirements and other guidance in product standards.

Condensation Interfaces

Number of condensation interfaces: 2

Distance of condensation interface 1 from the external surface: 100mm

Distance of condensation interface 2 from the external surface: 108.333333333333mm

Surface Condensation

Thermal quality Good. Mould growth unlikely.

 

Boundary Data

The Boundary data dialog can be accessed from the link on the info panel of the Condensation analysis tab. It allows the average monthly internal and external air temperature and relative humidity (RH) to be entered through a grid user interface as shown below.

 

 

The default external conditions come from CIBSE Guide A7, but they should be updated to reflect the actual local conditions.

 

You can load monthly external air temperature and RH values from the current site simulation weather data by clicking on the Load Simulation Weather Data button. Note that this is only enabled when site data has been loaded on the Simulation screen. The easiest way to achieve this if a simulation hasn't been run is to go to the Simulation screen, navigate to site level and press the Update toolbar icon.

 

The same condensation boundary data is stored for later use with this or other constructions.