Cooling Design Detailed Results
        The 'Analysis' tab has detailed half-hourly cooling 
 design results (displayed as a line graph by default).
         
        For more on how the output is calculated see: Calculation 
 of DesignBuilder Output from EnergyPlus Report Variables.
         
        
            - Air Temperature 
 - the calculated average temperature of the air.
 
            - Radiant Temperature 
  -  the (area * emissivity) weighted average of the zone inside surface temperatures. 
 
            - Operative Temperature 
 - The mean of the mean internal air and mean radiant temperatures.
 
            - Outside Dry-Bulb Temperature.
            
 
        
        
            - Glazing - the total 
 heat flow to the zone from the glazing, frame and divider of exterior 
 glazing excluding transmitted short-wave solar radiation (which is accounted 
 for in Solar Gains Exterior Windows below). 
 
 
        
         
        For windows without 
 an interior shading device this heat flow is equal to:
         
        + [Convective heat flow to the zone from 
 the zone side of the glazing]
        + [Net IR heat flow to the zone from zone 
 side of the glazing]
        – [Short-wave radiation from zone transmitted 
 back out the window]
        + [Conduction to zone from window frame and 
 divider, if present]
         
        Here, short-wave radiation is that from lights 
 and diffuse interior solar radiation.
         
        For windows with 
 an interior shading device this heat flow is equal to:
         
         [Convective 
 heat flow to the zone from the air flowing through the gap between glazing 
 and shading device]
        + [Convective heat flow to the zone from 
 the zone side of the shading device]
        + [Net IR heat flow to the zone from the 
 zone side of the glazing]
        + [Net IR heat flow to the zone from the 
 zone side of the shading device]
        – [Short-wave radiation from zone transmitted 
 back out the window]
        + [Conduction to zone from window frame and 
 divider, if present]
         
        
            - Walls - heat gain 
 due to conduction through all external walls, including the effect of 
 solar radiation and longwave radiation to the sky.
 
            - Roofs - heat gain 
 due to conduction through all external roofs, including the effect of 
 solar radiation and longwave radiation to the sky.
 
            - Ceilings (int) - 
 heat conduction gain through internal ceilings (e.g. zone above is colder).
 
            - Floors (int) - heat 
 conduction gain through internal floors (e.g. zone below is colder).
 
            - Floors (ext) - heat 
 conduction gain through external floors (not ground floor, e.g. floor 
 in cantilevered space, roof eaves etc).
 
            - Ground floors - 
 heat conduction gain through ground floors.
 
            - Partitions (int) 
 - heat conduction gain due to heat conduction through all internal partitions 
 from adjacent zones at different temperatures.
 
            - Doors and vents 
 - conduction heat gain through doors and vents.
 
        
        
        Airflow
        
            - Mech Vent + Nat Vent + 
 Infiltration - The sum of outside 
 air (in ac/h) flowing into the zone through:
 
            
                - The HVAC air distribution system +
 
                - Infiltration +
 
                - Natural ventilation
 
            
        
        System Heat Flows
        These heat flows are plotted on the System Energy axes:
         
        
            - Zone Heating - energy 
 supplied by local room heaters and reheat coils to maintain room internal 
 heating temperature setpoint temperature when using Detailed HVAC data.
 
            - Total Cooling - depending 
 on the Sizing method:
 
            
                - for the default ASHRAE 
 sizing method Total Cooling is the rate at which total energy (sensible 
 and latent) is removed from the mixed outside and return air stream in 
 order to bring the mixed air stream to the specified 
 temperature and humidity ratio of the supply air stream.
 
                - for the 2-Unitary DX
Sizing method - at building 
 level: sensible + latent cooling transfer to the supply air from 
 the AHU cooling coil + any single zone unitary and fan coil units in the 
 building. At zone level: sensible 
 + latent cooling transfer to the supply air from a single zone unitary 
 or fan coil unit.
 
            
            - Sensible Cooling - 
 depending on the Sizing method:
 
            
                - for the default ASHRAE 
 sizing method Sensible Cooling is the rate at which sensible energy is removed 
 from the mixed outside and return air stream in order to lower its temperature 
 to the specified temperature of 
 the supply air stream. Any energy needed for moisture addition or removal 
 is ignored.
 
                - for the 2-Unitary DX
Sizing method Sensible Cooling is sensible only cooling heat transfer from the cooling coil to the supply 
 air. Latent coil heat can be calculated as the difference: Total 
 Cooling - Sensible Cooling.
 
            
        
         
        Surface heat gain data refers to heat transfer from the inside surface 
 of the building elements to the zone.
         
        You can also customise the data and the way it is displayed using the 
 Display Options panel.