Openings tab in model data under External Glazing header
Airflow windows can be modelled by checking the Airflow windows option on the Openings tab. This option can be used to specify the control mechanism for windows in which forced air flows in the gap between adjacent layers of glass. Such windows are called “airflow windows.” They are also known as “heat-extract windows” or “climate windows.”
A common application is to reduce the zone load by exhausting indoor air through the window. In the cooling season this picks up and expels some of the solar heat absorbed by the window glass (and by the between-glass shade or blind, if present). In the heating season this warms the window, reducing the heat loss from the window. A side benefit is increased thermal comfort. This is because the inside surface of the window will generally be cooler in summer and warmer in winter.
The surface output variable Surface Window Gap Convective Heat Transfer Rate gives the heat picked up (or lost) by the gap airflow.
Gap airflow configurations for airflow windows:
(a) Air exhaust window: Airflow Source = 1-Indoor Air, Airflow Destination = 2-Outdoor air;
(b) Indoor air curtain window: Airflow Source = 1-Indoor air, Airflow Destination = 1-Indoor air;
(c) Air supply window: Airflow Source = 2-Outdoor air, Airflow Destination = 1-Indoor air;
(d) Outdoor air curtain window: Airflow Source = 2-Outdoor air, Airflow Destination = 2-Outdoor air;
(e) Airflow to Return Air: Airflow Source = 1-Indoor air, Airflow Destination = 3-Return air.
Based on “Active facades” Version no. 1, Belgian Building Research Institute, June 2002.
Note: Although Airflow control windows are defined under the External Glazing header (which normally holds data for wall glazing only) Airflow control window settings apply to all windows, including rooflights.
Check this option to include airflow control for external windows.
The source of the gap airflow. The choices are:
This is where the gap air goes after passing through the window. The choices are:
The diagram above shows the allowed combinations of Airflow source and Airflow destination. The allowed combinations of Airflow source and Airflow destination are:
The maximum value of the airflow (in m3/s per m of glazing width or ft3/min-ft). The value is typically 0.006 to 0.009 m3/s-m (4 to 6 ft3/min-ft). The airflow can be modulated through the Airflow multiplier schedule (below).
The fan energy used to move the air through the gap is generally very small and so is ignored.
The name of a schedule with values between 0.0 and 1.0. The timestep value of the airflow is Maximum flow rate times the schedule value.