The pond heat exchanger model represents a shallow pond with submerged hydronic tubes through which the heat transfer fluid is circulated. The model represents a "shallow" pond in that no attempt is made to model any stratification effects that may be present in deeper ponds.
This type of heat exchanger is intended to be connected to the supply side of a condenser loop, and can be used with any type of plant loop. The pond may be specified as the only heat exchanger on the condenser loop (as shown in top figure below) or it may be connected in parallel with other condenser loop heat exchangers (such as cooling towers, ground surface heat exchangers) as shown in the second figure below.
Pond heat exchanger as only heat exchanger on condenser loop
Pond heat exchanger with other heat exchangers on condenser loop
This alpha field contains the editable identifying name for the outside pond heat exchanger.
You can use this control to load data to the dialog from a pre-defined Ground heat exchanger template as a starting point for your particular component.
Note: After loading a Ground heat exchanger template it is important to make sure to update the Design heat exchanger flow rates as the sum of connected heat pump rated flow rates.
DesignBuilder provides 3 different ground heat exchanger types:
Note: The Type drop down list is not editable. To select a different type of heat exchanger, you must first select an appropriate template (above).
This numeric field contains the ground thermal conductivity (in W/mK or Btu-in/h-ft2-F).
This numeric field contains the pond depth (in m or ft).
This numeric field contains the pond area (in m2 or ft2).
This numeric field contains the hydronic tubing inside diameter (in m or in).
This numeric field contains the hydronic tubing outside diameter (in m or in).
This numeric field contains the hydronic tubing thermal conductivity (in W/mK or Btu-in/h-ft2-F).
This numeric field contains the number of hydronic tubing circuits, total in parallel in this pond.
This numeric field contains length (in m or ft) of each hydronic tubing circuit.