Office equipment gains

Activity tab in model data

 

Check the Office Equipment > On checkbox to include office equipment internal gains in the simulation.

Units

When the Gain definition level model option is set to 2-Zone by zone in model data you can select the units to be used for internal gains here on the Activity tab. Choose from the options:

 

Gain

Set the design level of energy consumption due to office equipment. Depending on the Equipment gain units model option setting, the gains data is entered either as Absolute zone power (in W) or as Power density (in W/m2 or W/ft2).

 

The fuel is assumed to be electricity, all gains are assumed to be emitted to the space.

Schedule

Select the schedule that governs the timing of gains in the zone. The level of gains are multiplied by the time-varying factor in this schedule to give the gain for each timestep in the simulation.

Radiant Fraction

This field is a decimal number between 0.0 and 1.0 and is used to characterise the amount of long-wave radiant heat being given off by office equipment in a zone. The radiant fraction will be multiplied by the total energy consumed by electric equipment to give the amount of long wavelength radiation gain from office equipment in a zone.

 

A value of zero means that the heat gain is entirely convective in which case all the heat is transferred to the air node in simulations.  A value of 1 means that the gain is entirely radiative in which case all the heat is distributed to the inside surfaces. a typical value is somewhere between 0.1 and 0.4.  

 

If the Internal gains operate with occupancy model option is not selected you can also set the operation schedule.