|   | 
 
 ThermalStorage:Ice:Simple ThermalStorage:Ice:Detailed 
 | 
 Used in: 
 
 | 
Ice thermal storage systems allow use of off-peak electricity to "charge" a storage tank of ice or other fluid and use that as a source of cooling to help reduce peak loads during periods of cooling demand. Two types of ice thermal storage systems can be modelled in DesignBuilder, simple and detailed, the latter option providing options to control the charge/discharge performance using curves.
This alpha field contains the identifying name for the ice storage tank.
Two types of ice thermal storage systems can be modelled in DesignBuilder:
All parameters below apply to the 2-Detailed option apart from Ice storage type below. The 1-Simple option only requires Name, Ice storage type and Capacity.
This setting applies only to the 1-Simple type of Ice thermal storage tank and specifies the type of ice storage tank to be modelled. There are two options:
Enter the maximum amount of latent thermal storage available in the ice storage system in GJ (Giga is 109) or ton-hrs. The removal or addition of sensible energy from the tank is not modelled, so the tank is always assumed to be at the freezing temperature of the storage material.
This setting defines the loss of ice stored during a particular hour. This field is dimensionless (per hour). It is not multiplied by any temperature difference between the tank and the environment in which it might be located.
This parameter defines the freezing/melting temperature of the ice storage medium (in °C or °F). For most tanks, this is simply 0.0°C (the default value). However, some tanks may use salts or other materials to change the freezing temperature. This can be changed using this parameter.
This input assists in more accurate modelling of the charging process by defining how the thawing of ice takes place. There are two options for this input:
For systems that have a charging process that does not vary significantly with fraction charged you can safely ignore this input by accepting the default value. The default value is 1-Outside melt.
Select the schedule that determines whether or not the ice storage system is available during a particular time period. This allows the system to be turned off during a particular season. A value of less than or equal to zero indicates that the ice storage system is not available. Any value greater than zero indicates that the system is available.
This field defines what timestep was used to produce the curve fits named in the previous inputs.
Note: This parameter is important because the curve fit is non-dimensional, so the data used to develop the curve fits were based on a specific length of time. In many cases, this is probably one hour or 1.0. The units for this parameter are hours.
The detailed ice storage model uses the performance curves to model performance. Currently, the only two allowed curve fit types for the detailed ice storage model are:
More information on this curve can be found in the section on Curves.
Select the curve to be used to model the charging process of the detailed ice storage system.
The amount of parasitic electric consumption (for controls or other miscellaneous electric consumption associate with the ice storage unit itself) during the charge phase. This parameter is dimensionless and gets multiplied by the current load on the tank.
The detailed ice storage model uses the performance curves to model performance. Currently, the only two allowed curve fit types for the detailed ice storage model are:
More information on this curve can be found in the section on Curves.
Select the curve to be used to model the discharging process of the detailed ice storage system.
The amount of parasitic electric consumption (for controls or other miscellaneous electric consumption associate with the ice storage unit itself) during the discharge phase. This parameter is dimensionless and gets multiplied by the current load on the tank.
Ice thermal storage can be either in parallel or in series to the chiller depending on the modelling requirements.
The parallel case should normally include two chillers, with one being the main chiller to operate during peak cooling time and the other being the chiller used to charge the tank during specified off peak time as long as conditions are favourable. The main chiller works in lower priority to the ice thermal storage and tops up cooling demand once ice thermal storage reaches its maximum capacity during discharging. Generally the charging chiller can be thought of as a "dummy" component because it does not physically exist in the real building and the main and charging chillers actually represent one single chiller.
For the series case, the chiller can be either upstream or downstream of the ice thermal storage. In both cases the ice tank can help reduce peak chiller demand:
Note: for upstream chillers, the capacity of the chiller is an especially important setting. When the chiller has a high capacity, it can meet the full cooling demand and the ice thermal storage does not need to operate. In this case, to see the effect of ice thermal storage, the chiller capacity must be relatively low. However the chiller size must be high enough to allow the chiller to deliver low enough outlet CHW temperature to charge the ice thermal storage tank.
The chilled water loop operation schemes include two Scheme operation type options that are suitable for modelling ice thermal storage objects: