Mixed mode Cooling
        In mixed mode buildings natural ventilation is used as the primary means 
 of providing cooling and, when this is inadequate to provide comfort conditions, 
 active cooling is introduced. 
         
        Definition of a mixed mode building:
         
        
            "It is a building in which occupants can open 
 windows, and which is designed with effective passive strategies for limiting 
 the effects of the external climate. The passively designed building is 
 utilised to provide acceptable conditions for the majority of the year, 
 and is supplemented by a mechanical system, either on an ‘as and when 
 required’ basis, or on a seasonal basis."
             
            Source: 
 Cooper, V.A., “Occupancy Comfort and Energy Consumption in Naturally 
 Ventilated and Mixed Mode Office Buildings”, PhD thesis, UMIST, 1998
             
            “Mixed-mode 
 refers to a hybrid approach to space conditioning that uses a combination 
 of natural ventilation from operable windows (either manually or automatically 
 controlled), and mechanical systems that include air distribution equipment 
 and refrigeration equipment for cooling. A well-designed mixed-mode building 
 begins with intelligent facade design to minimize cooling loads. It then 
 integrates the use of air-conditioning when and where it is necessary, 
 with the use of natural ventilation whenever it is feasible or desirable, 
 to maximize comfort while avoiding the significant energy use and operating 
 costs of year-round air conditioning."
            
             
            Source: 
 Mixed mode page on Center for Built 
 Environment website, contains background, case studies 
and a database 
 of 150 mixed mode buildings.
             
            Some useful background documents on mixed 
 mode design and simulation:
             
            
                - www.cbe.berkeley.edu/mixedmode
                
 
                - www.ibpsa.org/proceedings/BS1999/BS99_D-07.pdf
                
 
            
         
         
        DesignBuilder can model all three types of mixed mode system defined by CBE in the above reference.
         
        
            - Concurrent (Same space, same time)
                
Concurrent mixed-mode operation is  the most prevalent design strategy in practice today, in which the  air-conditioning system and operable windows operate in the same space and at  the same time. The HVAC system may serve as supplemental or “background”  ventilation and cooling while occupants are free to open windows based on  individual preference. Typical examples include open-plan office space with  standard VAV air-conditioning systems and operable windows, where perhaps  perimeter VAV zones may go to minimum air when sensor indicates that a window  has been opened.
 
            - Change-over (Same space, different times)
                
Change-over designs are  becoming increasingly common, where the building “changes-over” between natural  ventilation and air-conditioning on a seasonal or even daily basis. The building  automation system may determine the mode of operating based on outdoor  temperature, an occupancy sensor, a window (open or closed) sensor, or based on  operator commands. Typical examples include individual offices with operable  windows and personal air conditioning units that shut down for a given office  anytime a sensor indicates that a window has been opened; or a building envelope  where automatic louvers open to provide natural ventilation when the HVAC system  is in economizer mode, and then close when the system is in cooling or heating  mode. 
            - Zoned (Different spaces, same time)
                
Zoned systems are also common,  where different zones within the building have different conditioning  strategies. Typical examples include naturally ventilated office buildings with  operable windows and a ducted heating/ventilation system, or supplemental  mechanical cooling provided only to conference rooms. For many mixed-mode  buildings, operating conditions sometimes deviate somewhat from their original  design intent (e.g., a building originally designed for seasonal changeover  between air-conditioning and natural ventilation may, in practice, operate both  systems concurrently).  
        
        Note: Concurrent and Zoned systems can be modelled simply by including natural ventilation with HVAC systems without using DesignBuilder mixed mode control. In DesignBuilder "mixed mode" specifically refers to Change-over systems where the HVAC and the natural ventilation do not take place at the same time.
         
        
        
         
        DesignBuilder supports mixed mode in all combinations of natural ventilation and HVAC model options.
         
        The steps to setting up a change-over mixed mode model in DesignBuilder are:
         
        
            - Include active cooling and natural ventilation 
 by switching on the Natural ventilation 
 on and Cooled options on the HVAC tab. 
 
 
            - Also, include mechanical ventilation if there 
 is outside air introduced through the HVAC system.
 
            - Ensure that the setpoints 
 for natural ventilation and cooling operation are correct. The 
 natural ventilation (window/vent opening) setpoint should ideally be 2°C lower than 
 the cooling setpoint to ensure maximum use of natural ventilation and 
 to avoid the active cooling system being used unnecessarily and also 2°C higher than the heating .temperature. Typical values might be heating setpoint temperature = 21°C, natural ventilation setpoint temperature = 23°C, cooling setpoint temperature = 25°C. Heating should ideally be switched off in the summer to avoid unnecessary heating caused by natural ventilation overcooling the space.
 
            - See the mixed mode section on the HVAC help for detailed information on the data that can be set, including conditions that require windows and vents to be closed such as rain, wind and low outside air temperature.
 
        
        Note: "Mixed mode" means the same as the term "Hybrid ventilation" used in the EnergyPlus documentation.