EnergyPlus Daylight Calculations
        The EnergyPlus daylighting model, in conjunction with the thermal analysis, 
 determines the energy impact of daylighting strategies based on analysis 
 of daylight availability, site conditions, window management in response 
 to solar gain and glare, and various lighting control strategies.
         
        The daylighting calculations are carried out during the simulation in 
 3 main steps:
          
        
            - Daylight factors, which are ratios of interior 
 illuminance or luminance to exterior horizontal illuminance, are calculated 
 and stored. The user specifies the coordinates of one or two reference 
 points in each daylit zone. EnergyPlus then integrates over the area of 
 each exterior window in the zone to obtain the contribution of direct 
 light from the window to the illuminance at the reference points, and 
 the contribution of light that reflects from the walls, floor and ceiling 
 before reaching the reference points. Window luminance and window background 
 luminance, which are used to determine glare, are also calculated. Taken 
 into account are such factors as sky luminance distribution, window size 
 and orientation, glazing transmittance, inside surface reflectances, sun 
 control devices such as movable window shades, and external obstructions. 
 Dividing daylight illuminance or luminance by exterior illuminance yields 
 daylight factors. These factors are calculated for the hourly sun positions 
 on sun-paths for representative days of the run period.
 
            - A daylighting calculation is performed each heat-balance 
 time step when the sun is up. In this calculation the illuminance at the 
 reference points in each zone is found by interpolating the stored daylight 
 factors using the current time step’s sun position and sky condition, 
 then multiplying by the exterior horizontal illuminance. If glare control 
 has been specified, the program will automatically deploy window shading, 
 if available, to decrease glare below a specified comfort level. A similar 
 option uses window shades to automatically control solar gain.
 
            - The electric lighting control system is simulated 
 to determine the lighting energy needed to make up the difference between 
 the daylighting illuminance level and the design illuminance. Finally, 
 the zone lighting electric reduction factor is passed to the thermal calculation, 
 which uses this factor to reduce the heat gain from lights. The EnergyPlus 
 daylighting calculation is derived from the daylighting calculation in 
 DOE-2.1E, which is described in [Winkelmann, 1983] and [Winkelmann and 
 Selkowitz, 1985]. There are two major differences between the two implementations: 
 (1) In EnergyPlus daylight factors are calculated for four different sky 
 types—clear, clear turbid, intermediate, and overcast; in DOE-2 only two 
 sky types are used—clear and overcast. (2) In EnergyPlus the clear-sky 
 daylight factors are calculated for hourly sun-path sun positions several 
 times a year whereas in DOE-2 these daylight factors are calculated for 
 a set of 20 sun positions that span the annual range of sun positions 
 for a given geographical location.