This topic describes the BREEAM-specific Daylighting Calculation options which can be accessed when the Simulation type is set to 3-BREEAM.
Check this checkbox if you would like to run an annual daylighting simulation suitable for assessing credits for BREEAM Health and Wellbeing Credit HEA 01 option 4b .
Check this checkbox if you would like to run a point in time illuminance daylighting simulation suitable for assessing credits for BREEAM Health and Wellbeing Credit HEA 01 option 4a .
By default the occupancy schedule used for each zone in the Annual simulations are based on the zone Occupancy schedule defined on the Activity tab, however you can override this to use the same occupancy schedule for each zone by selecting this option and selecting the schedule in the browse control below.
When the above Override zone occupancy schedule option is selected, you can select the occupancy schedule to be used to define when zones are occupied for all zones in the simulation. Values in the schedule greater than 0 indicate occupancy.
The default occupancy schedule provided by DesignBuilder does not include daylight saving time (DST). DST has to be added manually to the schedule. For example for the Northern Hemisphere you can use a schedule like the following:
            
Schedule:Compact,
8:00 - 18:00 Every day (DST Northern Hemisphere),
Fraction,
Through: 03/30,
For: AllDays,
Until: 08:00, 0,
Until: 18:00, 1,
Until: 24:00, 0,
Through: 10/26,
For: AllDays,
Until: 07:00, 0,
Until: 17:00, 1,
Until: 24:00, 0,
Through: 12/31,
For: AllDays,
Until: 08:00, 0,
Until: 18:00, 1,
Until: 24:00, 0;
For BREEAM HEA 01 Option 4b, you can to enter a minimum illuminance threshold value from Table 12 based on the area type of the zones being analysed.
For BREEAM HEA 01 Option 4b, you can enter an average illuminance threshold value from Table 12 based on the area type of the zones being analysed.
BREEAM annual daylighting calculations do not apply LM-83-12 dynamic shading or any other window shading algorithms. Any Window shading settings on the Openings tab are ignored.
In general you should make the following settings for BREEAM point in time daylighting calculations.
Sky method: 1-Standard sky
Sky model: 6-CIE overcast day (specify illuminance)
Zenith illuminance: 10000
There are 2 general methods for generating the sky illuminance distribution for the Radiance calculation:
When the Sky method is set to 2-Perez all weather there are 4 methods to choose from depending on the data you have available. In all cases the time, day and month of the analysis must be set to define the location of the sun in the sky.
3-Direct horizontal irradiance for when measured (or calculated) direct horizontal and diffuse horizontal irradiance data is available. Such data can usually be found in EnergyPlus epw files in W/m2.
Perez sky clearness (ε). Enter a value from 1.0 to 12.0.
Available only when using the 2-Perez all weather Sky method and the 1-Brightness and clearness Perez method
Perez sky brightness (Δ). Enter a value from 0.01 to 0.6.
Available only when using the 2-Perez all weather Sky method and the 1-Brightness and clearness Perez method
The direct normal solar broad spectrum irradiance (in W/m2 or W/ft2). This value can be found from the site level hourly weather data.
Available only when using the 2-Perez all weather Sky method and the 2-Direct normal irradiance Perez method.
The diffuse horizontal solar broad spectrum irradiance (in W/m2 or W/ft2). This value can be found from the site level hourly weather data.
Available only when using the 2-Perez all weather Sky method and the 2-Direct normal irradiance or 3-Direct horizontal irradiance Perez method have been selected.
The direct normal illuminance (visible spectrum) (in lux or fc).
Available only when using the 2-Perez all weather Sky method and the 4-Direct normal illuminance Perez method
The diffuse horizontal illuminance (visible spectrum) (in lux or fc).
Available only when using the 2-Perez all weather Sky method and the 4-Direct normal illuminance Perez method
When using the 1-Standard sky Sky method, select the sky model to be used for the daylighting calculations. Select from:
Sky luminance profiles for 3 sky models (Source Rendering with Radiance: A Practical Tool for Global Illumination)
When using the 1-Standard sky Sky method and one of the sunny or intermediate Sky models (options 1-4), you must define the position of the sun by entering the Month, Day of the month and Hour.
When the Sky model (above) is set to 6-CIE overcast day (scaled) you can define the scaling illuminance at the Zenith (in lux or fc). The default is 10,000 lux which allows daylight factors to be calculated simply as working plane illuminance values divided by 100.