When using the VAV cooling sizing method, the Cooling design calculation is made through a detailed EnergyPlus simulation using Compact HVAC VAV equipment. A diagram of the system layout used is shown in the VAV topic.
Each zone has it's own VAV AHU with a fan (generating no pickup), a water-cooled AHU cooling coil, an outside air controller and a zone terminal box with a damper to reduce supply air flow. More specifically:
Unlike the ASHRAE cooling sizing option, VAV can be used in conjunction with Natural ventilation.
The constant dry-bulb air temperature of the air supplied for cooling the zone
The Design turndown ratio is the fraction that the zone VAV box can reduce to based on the supply air maximum flow rate. It is normally specified to meet the minimum ventilation requirement for the occupants. A value of 1.0 means that the VAV box cannot reduce supply air at all (i.e. it is a constant volume system).
Turndown ratio is typically in range 0.3 - 0.5. Minimum is 0 and maximum is 1.