In the ASHRAE cooling sizing method the cooling design load calculations are carried out using the standard ASHRAE Heat Balance method implemented in EnergyPlus using the 'ZoneHVAC:IdealLoadsAirSystem' system type. You can define the conditions of the supply air delivered to cooled zones using Design supply temperature and Supply air humidity ratio. The total (sensible + latent) load is calculated as the enthalpy change between the zone return air and the specified supply air condition for the current load.
The ASHRAE system is modelled assuming:
Cautionary Note: The Ideal Loads Air System component does not control zone humidity levels. The Ideal Loads Air System component total cooling load is simply the enthalpy change between the return air and the user-specified supply air condition for the current load. The latent load is the total load less the sensible load and may be positive or negative.
The constant dry-bulb air temperature of the air supplied for cooling the zone.
The constant humidity ratio (mass of water per mass of dry air) of the cold supply air to be delivered when cooling is required. The default humidity ratio is 0.008. You should be careful to enter a value that is a valid condition, i.e. it is under the 100% saturation line on the Psychrometric Chart.
Cautionary Note: The EnergyPlus Ideal Loads Air System component used for these calculations does not control zone humidity levels. Total cooling load is simply calculated as the enthalpy change between the return air condition and the user-specified supply air condition for the current load. The latent load is the total load less the sensible load and may be positive or negative.