This field contains the unique identifying name for the heating side of the plant loop heat pump.
DesignBuilder provides the following plant loop heat pump types:
1-Equation fit water to water heat pump - corresponds to the EnergyPlus Equation fit model.
2-Plant loop EIR heat pump - for modelling water to water or air to water heat pumps based on the EIR formulation.
Tip: For both these heat pump types, it is important to use manufacturer's performance data to ensure the accuracy of your simulations.
The Equation fit model uses four non-dimensional equations (curves) to predict the heat pump performance in cooling and heating modes. The methodology involves using the generalised least square method to generate a set of performance coefficients from the catalogue data at indicated reference conditions. Then the respective coefficients and indicated reference conditions are used in the model to simulate the heat pump performance. The variables that influenced the water-to-water heat pump performance are load side inlet water temperature, source side inlet temperature, source side water flow rate and load side water flow rate.
You can load data to the dialog from a pre-defined heat pump template as a starting point for your particular heat pump component. A sample list of manufacturers data is provided in the templates and instructions on how to create your own templates from manufacturers data.
Heat pumps are usually selected using their Rated heating capacity.
This setting is used if the Reference heating power consumption is set to autosize. The nominal COP is defined by the Reference heating capacity divided by the corresponding Reference heating power consumption and is non-dimensional. This field is only used for sizing; if the Reference power consumption is set to a fixed value then the COP of the component during simulation will be determined by the ratio of Reference heating capacity divided by the corresponding Reference heating power consumption and not by the value in this field. This COP does not include power for fluid circulation pumps, it is just for the heat pump itself.
This setting allows a sizing factor for this component to be specified. The sizing factor is used when the component design inputs are autosized: the autosizing calculations are performed as usual and the results are multiplied by the sizing factor. The Sizing factor allows a component to be sized to meet part of the plant loop’s design load while continuing to use the autosizing feature. For example if there are two heat pumps on the supply side, each one could be sized to be half of the design load.
This autosizeable setting contains the rated volumetric flow rate on the load side of the heat pump in (m3/s or gal/min). This corresponds to the highest load side heat transfer rate listed in the catalogue data.
This autosizeable setting contains the rated volumetric flow rate on the source side of the heat pump in (m3/s or gal/min). This corresponds to the highest load side heat transfer rate listed in the catalogue data.
This autosizeable setting contains the rated heating capacity of the heat pump in W. This corresponds to the highest load side heat transfer rate listed in the catalogue data.
This autosizeable setting contains the rated power consumption of the heat pump in W. This corresponds to the highest load side heat transfer rate listed in the catalogue data.
Select a Quad Linear Performance curve to be used to define the heating capacity of this heat pump at runtime.
More details on how these coefficients are used are provided in the technical section of the Water to water heat pumps page and in the Engineering Reference.
Select a Quad Linear Performance curve to define the Heating compressor power curve. More details on how these coefficients in the curve are used are described in the Engineering Reference.
This optional selection allows you to specify the companion cooling water to water heat pump for this heating component. This should be the name of an Equation Fit heat pump cooling component on the same plant loop. Because the cooling and heating models are often intended to represent separate operating modes of one single reversible heat pump, it is useful to identify the corresponding cooling heat pump. This is used with autosizing so that the sizing calculations can be coordinated ensuring that the two companion heat pumps get the same design reference flow rates.
The plant loop EIR model is based on the same formulation used in the EIR chiller model. This allows curves specifying capacity and energy usage to be defined generically, enabling them to be applicable to a wide variety of components. In this model, the curve can be a quadratic function of temperatures or an even more generic lookup table.
Tip: Note: The EIR model is more flexible than the Equation fit model. It can be operated either as a water-sourced heat pump with the source side connected to another plant loop or as an air-sourced heat pump with the source side interacting with the outdoor air.
Data for this component is also considered to be easier to obtain than for the Equation fit model.
Note: This component is currently a constant flow device (it will always request its full design flow from the plant). A future addition is planned to make it respond to outlet setpoint in order to vary the flow request.
This setting contains the reference COP for this unit, which is used when calculating the power required for the heat pump under simulation conditions. The COP is defined as the load side energy transfer divided by the power input, with dimensionless units of [W/W].
This setting allows the the sizing of this unit to be scaled relative to the plant-determined autosized flow and heat capacity.
This autosizable setting defines the reference load side flow rate for the heat pump. This field is used as the nominal flow request for this heat pump unit during the simulation. The units for this field are (m3/s or gal/min).
This autosizable setting defines the reference source side flow rate for the heat pump. This field is used as the nominal flow request for this heat pump unit during the simulation. The units for this field are (m3/s or gal/min).
Important Note: For air source heat pumps, the Source side reference flow rate is an air flow rate, whereas for water to water heat pumps it is a water flow rate. Water source side reference flow rates will typical be much lower than Air source reference air flow rates.
This autosizable setting defines the heat pump's reference load side heating capacity (in W).
Select a Bivariate curve or table that defines an available capacity modifier of the unit as a function of the load side outlet temperature and the source side inlet temperature. The temperatures are in °C when used in the function and the output of the function is multiplied by the reference capacity to get a current available capacity.
Select a Bivariate curve or table that defines an EIR (1/COP) modifier as a function of the load side outlet temperature and the source side inlet temperature. The temperatures are in °C when used in the function. The output of this function and the output of the EIR Modifier Function of PLR are multiplied by the reference EIR to get a current EIR .
Select a Univariate curve or table that defines an EIR modifier as a function of the current part load ratio. The output of this function and the output of the EIR Modifier Function of Temperature are multiplied by the reference EIR to get a current EIR .
Select the heat pump’s condenser type. Options are:
1-Air Source - for an air to water heat pump
2-Water Source for a water to water heat pump