Performance Curves

 

Curve:Linear

Curve:QuadLinear

Curve:QuintLinear

Curve:Quadratic

Curve:Cubic

Curve:Quartic

Curve:Exponent

Curve:Bicubic

Curve:Biquadratic

Curve:RectangularHyperbola2

Curve:DoubleExponentialDecay

 

Used in many HVAC components as well as electrical storage devices

 

In EnergyPlus HVAC, performance curves are the mathematical mechanism that adjusts rated equipment performance (capacity, efficiency, airflow effects, etc.) as operating conditions change based on actual operating conditions. They are needed because most HVAC equipment does not operate at its rated capacity or efficiency except at laboratory reference conditions. In more detail, performance curves:

 

 

DesignBuilder performance curves consist of a range of different polynomial curve types that are used to characterise the performance of HVAC equipment. Several other non-polynomial curves are also included to characterize the performance of pumps and fans. The curves are usually derived from fits or regressions to data covering a limited range. Results for independent variable values outside this range are likely to be invalid, so curve input always contains a range of validity (maximum and minimum permitted values) for each independent variable and can optionally have limits on the curve output. No error or warning message is issued if an independent variable is outside the range. Instead, EnergyPlus uses the minimum value if an independent variable is less than the minimum, and the maximum if a variable exceeds the maximum. Similarly, no error or warning message is issued if the curve output is outside the range of the optional minimum and maximum curve output limits. Instead, EnergyPlus uses the minimum and maximum curve limits to cap the output of the performance curve.

Tip: For guidance on how to generate the data required for Performance curves see: Performance Curve Coefficient Tools

General Tab

On the General tab you can set the curve type and enter the curve coefficients.

 

The curve data follow a similar pattern and all have the same first 4 data items:

Name

A user assigned unique name for a curve. When a curve is used, it is referenced by this name.

Note

Specific information about the curve.

Source

The source setting defines the origin of the curve. For most library curves provided with the software, the source is usually either "EnergyPlus", meaning it comes from the EnergyPlus curves database, which is largely derived from the DOE-2 database, or "DesignBuilder" meaning that the curve is provided by DesignBuilder Software.

Category

The category can be one of:

The rest of the data depends on the curve Category setting, as described below.

Linear

Input for the linear curve consists of a curve name, the two coefficients, and the maximum and minimum valid independent variable values. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g. limit extrapolation). The equation represented by the linear curve is:

y = C1 + C2 * x

Coefficient 1 constant

The constant coefficient (C1) in the equation.

Coefficient 2 x

The linear coefficient (C2) in the equation.

Minimum value of x

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This field is used to indicate the kind of units that may be associated with the x values. It is used by editor to display the appropriate SI and IP units for the Minimum value of x and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select Dimensionless which will have no unit conversion.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Quad Linear

Input consists of the curve name, the five coefficients, and maximum and minimum values for each of the independent variables. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g., limit extrapolation). The equation is represented by this curve:

 

y = C1 + C2 * w + C3 * x + C4 * y + C5 * z

Name

A user assigned unique name for an instance of this curve. When a curve of this type is used, it is referenced by this name.

Coefficient1 Constant

The constant coefficient (C1) in the equation.

Coefficient2 w

The coefficient (C2) in the equation.

Coefficient3 x

The coefficient (C3) in the equation.

Coefficient4 y

The coefficient (C4) in the equation.

Coefficient5 z

The coefficient (C5) in the equation.

MinimumW

The minimum allowable value of w. Values of w less than the minimum will be replaced by the minimum.

MaximumW

The maximum allowable value of w. Values of w greater than the maximum will be replaced by the maximum.

MinimumX

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

MaximumX

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

MinimumY

The minimum allowable value of y. Values of y less than the minimum will be replaced by the minimum.

MaximumY

The maximum allowable value of y. Values of y greater than the maximum will be replaced by the maximum.

MinimumZ

The minimum allowable value of z. Values of z less than the minimum will be replaced by the minimum.

MaximumZ

The maximum allowable value of z. Values of z greater than the maximum will be replaced by the maximum.

Input unit type for W

This field is used to indicate the kind of units that may be associated with the w values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of w and Maximum value of w. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Input unit type for X

This field is used to indicate the kind of units that may be associated with the x values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of x and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Input unit type for Y

This field is used to indicate the kind of units that may be associated with the y values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of y and Maximum value of y. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Input unit type for Z

This field is used to indicate the kind of units that may be associated with the z values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of z and Maximum value of z. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Quint Linear

Input consists of the curve name, the six coefficients, and maximum and minimum values for each of the independent variables. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g., limit extrapolation). The equation is represented by this curve:

 

y = C1 + C2 * v + C3 * w + C4 * x + C5 * y + C6 * z

Name

A user assigned unique name for an instance of this curve. When a curve of this type is used, it is referenced by this name.

Coefficient1 Constant

The constant coefficient (C1) in the equation.

Coefficient2 v

The coefficient (C2) in the equation.

Coefficient3 w

The coefficient (C3) in the equation.

Coefficient4 x

The coefficient (C4) in the equation.

Coefficient5 y

The coefficient (C5) in the equation.

Coefficient6 z

The coefficient (C6) in the equation.

MinimumV

The minimum allowable value of v. Values of v less than the minimum will be replaced by the minimum.

MaximumV

The maximum allowable value of v. Values of v greater than the maximum will be replaced by the maximum.

MinimumW

The minimum allowable value of w. Values of w less than the minimum will be replaced by the minimum.

MaximumW

The maximum allowable value of w. Values of w greater than the maximum will be replaced by the maximum.

MinimumX

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

MaximumX

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

MinimumY

The minimum allowable value of y. Values of y less than the minimum will be replaced by the minimum.

MaximumY

The maximum allowable value of y. Values of y greater than the maximum will be replaced by the maximum.

MinimumZ

The minimum allowable value of z. Values of z less than the minimum will be replaced by the minimum.

MaximumZ

The maximum allowable value of z. Values of z greater than the maximum will be replaced by the maximum.

Input unit type for V

This field is used to indicate the kind of units that may be associated with the v values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of v and Maximum value of v. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Input unit type for W

This field is used to indicate the kind of units that may be associated with the w values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of w and Maximum value of w. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Input unit type for X

This field is used to indicate the kind of units that may be associated with the x values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of x and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Input unit type for Y

This field is used to indicate the kind of units that may be associated with the y values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of y and Maximum value of y. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Input Unit Type for Z

This field is used to indicate the kind of units that may be associated with the z values. It is used by the editor to display the appropriate SI and IP units for the Minimum value of z and Maximum value of z. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

 

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Quadratic

Input for a quadratic curve consists of the curve name, the three coefficients, and the maximum and minimum valid independent variable values. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g. limit extrapolation). The equation represented by the quadratic curve is:

y = C1 + C2 * x + C3 * x2

Coefficient 1 constant

The constant coefficient (C1) in the equation.

Coefficient 2 x

The linear coefficient (C2) in the equation.

Coefficient 3 x2

The quadratic coefficient (C3) in the equation.

Minimum value of x

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This field is used to indicate the kind of units that may be associated with the x values. It is used by editor to display the appropriate SI and IP units for the Minimum value of x and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Cubic

Input for a cubic curve consists of the curve name, the 4 coefficients, and the maximum and minimum valid independent variable values. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g. limit extrapolation). The equation represented by the cubic curve is:

y = C1 + C2 * x + C3 * x2 + C4 * x3

Coefficient 1 constant

The constant coefficient (C1) in the equation.

Coefficient 2 x

The linear coefficient (C2) in the equation.

Coefficient 3 x2

The quadratic coefficient (C3) in the equation.

Coefficient 4 x3

The quadratic coefficient (C4) in the equation.

Minimum value of x

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This field is used to indicate the kind of units that may be associated with the x values. It is used by editor to display the appropriate SI and IP units for the Minimum value of x and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Exponent

Input for a exponent curve consists of the curve name, the 3 coefficients, and the maximum and minimum valid independent variable values. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g. limit extrapolation). The equation represented by the exponent curve is:

y = C1 + C2 * xC3

Coefficient 1 constant

The constant coefficient (C1) in the equation.

Coefficient 2 constant

The linear coefficient (C2) in the equation.

Coefficient 3 constant

The exponent coefficient (C3) in the equation.

Minimum value of x

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This field is used to indicate the kind of units that may be associated with the x values. It is used by editor to display the appropriate SI and IP units for the Minimum value of x and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Bi-quadratic

This curve is a function of two independent variables. Input consists of the curve name, the six coefficients, and min and max values for each of the independent variables. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g. limit extrapolation). The equation represented by the biquadratic curve is:

z = C1 + C2 * x + C3 * x2 + C4* y + C5 * y2 + C6*xy

Coefficient 1 constant

The constant coefficient (C1) in the equation.

Coefficient 2 x

The linear coefficient (C2) in the equation.

Coefficient 3 x2

The quadratic coefficient (C3) in the equation.

Coefficient 4 y

The coefficient C4 in the equation.

Coefficient 5 y2

The coefficient C5 in the equation.

Coefficient 6 xy

The coefficient C6 in the equation.

Minimum value of x

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum value of y

The minimum allowable value of y. Values of y less than the minimum will be replaced by the minimum.

Maximum value of y

The maximum allowable value of y. Values of y greater than the maximum will be replaced by the maximum.

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This field is used to indicate the kind of units that may be associated with the x values. It is used by editor to display the appropriate SI and IP units for the Minimum value of x and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Input unit type for y

This field is used to indicate the kind of units that may be associated with the y values. It is used by editor to display the appropriate SI and IP units for the Minimum value of y and Maximum value of y. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Bi-cubic

This curve type is a function of two independent variables. Input consists of the curve name, the ten coefficients, and the minimum and maximum values for each of the independent variables. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g. limit extrapolation). The equation represented by the bicubic curve is:

z = C1 + C2 * x + C3* x2 + C4* y + C5 * y2 + C6*xy + C7* x3 + C8* y3 + C9 * x2y + C10 * xy2

Coefficient 1 constant

The constant coefficient (C1) in the equation.

Coefficient 2 x

The linear coefficient (C2) in the equation.

Coefficient 3 x2

The quadratic coefficient (C3) in the equation.

Coefficient 4 y

The coefficient C4 in the equation.

Coefficient 5 y2

The coefficient C5 in the equation.

Coefficient 6 xy

The coefficient C6 in the equation.

Coefficient 7 x3

The coefficient C7 in the equation.

Coefficient 8 y3

The coefficient C8 in the equation.

Coefficient 9 x2y

The coefficient C9 in the equation.

Coefficient 10 xy2

The coefficient C10 in the equation.

Minimum value of x

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum value of y

The minimum allowable value of y. Values of y less than the minimum will be replaced by the minimum.

Maximum value of y

The maximum allowable value of y. Values of y greater than the maximum will be replaced by the maximum.

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This field is used to indicate the kind of units that may be associated with the x values. It is used by editor to display the appropriate SI and IP units for the Minimum value of X and Maximum value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Input unit type for y

This field is used to indicate the kind of units that may be associated with the y values. It is used by editor to display the appropriate SI and IP units for the Minimum Value of y and Maximum Value of y. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Quartic

Input for a Quartic (fourth order polynomial) curve consists of the curve name, the five coefficients, and the maximum and minimum valid independent variable values. Optional inputs for curve minimum and maximum may be used to limit the output of the performance curve (e.g., limit extrapolation). The equation represented by the quartic curve is:

 

y = C1 + C2 * x + C3 * x2 + C4 * x3 + C5 * x4

 

Coefficient 1 constant

The constant coefficient (C1) in the equation.

Coefficient 2 x

The linear coefficient (C2) in the equation.

Coefficient 3 x2

The quadratic coefficient (C3) in the equation.

Coefficient 4 x3

The cubic coefficient (C4) in the equation.

Coefficient 5 x4

The fourth-order coefficient (C5) in the equation.

Minimum value of x

The minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum curve output

The minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum value of x

The maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This field is used to indicate the kind of units that may be associated with the x values. It is used by IDF Editor to display the appropriate SI and IP units for the Minimum Value of X and Maximum Value of x. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select Dimensionless which will have no unit conversion.

 

Output unit type

This field is used to indicate the kind of units that may be associated with the output values. It is used by the editor to display the appropriate SI and IP units for the Minimum curve output and Maximum curve output. The unit conversion is not applied to the coefficients. The available options are shown below. If none of these options are appropriate, select 1-Dimensionless which will have no unit conversion.

Rectangular Hyperbola 2

Input for the single rectangular hyperbola type 2 curve consists of the curve name, the three coefficients, and the maximum and minimum valid independent variable values. Optional inputs for the curve minimum and maximum may be used to limit the output of the performance curve (e.g., limit extrapolation). The equation is:

 

y = (C1* x) / (C2 + x) + C3* x

 

Coefficient 1 C1

The required numeric constant coefficient C1 in the equation.

Coefficient 2 C2

The required numeric constant coefficient C2 in the equation.

Coefficient 3 C3

The required numeric constant coefficient C3 in the equation.

Minimum value of x

The required numeric minimum allowable value of x. Values of x less than the minimum will b e replaced by the minimum.

Maximum value of x

The required numeric maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum.

Minimum curve output

The optional numeric minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum.

Maximum curve output

The optional numeric maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

This optional field is provided for future purposes so that DesignBuilder could display the appropriate SI or IP units for the Minimum value of x and Maximum value of x (currently dimensionless). At this time, only the Dimensionless option is provided so that no unit conversion is used for this curve.

Output unit type

This optional field is provided for future purposes so that DesignBuilder could display the appropriate SI or IP units for the Minimum curve output and Maximum curve output (currently dimensionless). At this time, only the 1-Dimensionless option is provided so that no unit conversion is used for this curve.

Double Exponential Decay

Input for the double exponential decay curve consists of the curve name, the five coefficients, and the maximum and minimum valid independent variable values. Optional inputs for the curve include the minimum and maximum output of the performance curve. The equation is:

 

y = C1 + C2 exp( C3 x) + C4 exp(C5 x)

Coefficient 1 C1

The required numeric constant coefficient C1 in the equation.

Coefficient 2 C2

The required numeric constant coefficient C2 in the equation.

Coefficient 3 C3

The required numeric constant coefficient C3 in the equation.

Coefficient 4 C4

The required numeric constant coefficient C4 in the equation.

Coefficient 5 C5

The required numeric constant coefficient C5 in the equation.

Minimum value of x

The required numeric minimum allowable value of x. Values of x less than the minimum will be replaced by the minimum

Maximum value of x

The required numeric maximum allowable value of x. Values of x greater than the maximum will be replaced by the maximum

Minimum curve output

The optional numeric minimum allowable value of the evaluated curve. Values less than the minimum will be replaced by the minimum

Maximum curve output

The optional numeric maximum allowable value of the evaluated curve. Values greater than the maximum will be replaced by the maximum.

Input unit type for x

The optional field is provided for future purposes so that DesignBuilder could display the appropriate SI or IP units for the Minimum and Maximum value of x. Currently, only Dimensionless option is provided so that no unit conversion is used for this curve

Output unit type

The optional field is provided for future purposes so that DesignBuilder could display the appropriate SI or IP units for the Minimum and Maximum curve output. Currently, only the 1-Dimensionless option is provided so that no unit conversion is used for this curve.

Curve Plot Tab

Click on the Curve Plot tab to view the performance curve data in graphical form.