CIBSE TM59:2017 - Modelling and Analysis Guide

TM59:2017 is a standardised approach to predicting overheating risk for residential building designs (new-build or major refurbishment) using dynamic thermal analysis. The testing of the methodology has focused on flats, as they tend to represent a higher overheating risk than houses. However, the methodology is also applicable to houses.

Overview

This guide summarises the key points in the CIBSE TM59:2017 methodology and provides a commented example of the DesignBuilder TM59 analysis workflow. It is divided into the following sections:

 

 

The modelling example starts after the model geometry has been completed (including construction and opening assignment).

 

Note: this guide does not include all of the details required to build, simulate and assess a model according to TM59 2017 and it’s still necessary to refer to the TM59 Design methodology for the assessment of overheating risk in homes standard itself.

TM59 Modelling process

Weather data

The Design Summer Year (DSY) file to use is prescribed per location in CIBSE TM59 Weather file requirements (CIBSE, 2026a), section 1.3. Use the DSY it specifies for the building's location, import it through Add new hourly weather data, and check the correct file is loaded before running. CIBSE will update the files and guidance as new weather projections emerge, so you should check you are using the correct data for each project.

 

Since 2017, the minimum requirement for TM59 simulations is to use DSY1 Future weather data for the nearest location and the 2020s, High emissions, 50th % percentile scenario.

Note: Although 2020 is clearly a previous year it is still considered to be "future" weather data in TM59 since this aspect of the standard was conceived back in 2017.

Tip: You can obtain CIBSE Future 2016 weather files suitable for use in TM59 analyses from the DesignBuilder CIBSE weather file page.

The DSY weather data files required for the simulations can be imported using the approach described on the Add new hourly weather data help page.

Exposure type

This setting affects the calculated natural ventilation flow rates and should reflect the real site. The appropriate site exposure type can be set at site level on the Location tab > Site Details > Exposure to wind.

Air speed

According to TM59 chapter 3.6, the modelled air speed should be set to 0.1 m/s. This is the value used where no elevated air movement is present.To meet this requirement, an appropriate Air velocity schedule can be set at building level on the Activity tab to define air speed in all zones.

Setting up Model options

Adjust the default model options so the pre-defined TM59 activity templates behave correctly:

 

Setting Value Model Options tab Header Explanation
Gains data Early Data Gains Data Aligns gain profiles with the TM59 templates.
Occupancy method 3-Number of people Data Gains Data Uses fixed people counts per the templates.
Occupancy latent gains 2-Fixed fraction Data Gains Data

According to TM59 chapter 5.1: “A maximum sensible heat 75 W/person and a maximum latent heat gain of 55 W/person are assumed in living spaces”.

Setting the Occupancy latent gains to 2-Fixed fraction ensures that the simulated occupancy gains will be aligned with the standard, i.e. the 75/55W ratio will be always used.

Equipment gain units 2-Absolute zone power Data Gains Data Absolute equipment gains per zone.
Lighting gain units 1-Power density Data Gains Data Power-density lighting loads (TM59 ch. 5.2).
Natural ventilation Calculated Data Natural Ventilation and Infiltration Required for airflow-network window control.
Lump similar windows on surface Unchecked Advanced Simplification

Keeps per-window control settings distinct. Similar windows on the same surface should not be lumped to allow each window to have its own settings.

Working with TM59 templates

To reduce the amount of work necessary to set up the occupant and equipment gain profiles, a set of TM59 Activity templates are provided. These can be found in the “Residential spaces” activity folder.

 

 

Selecting the right Activity template ensures that the correct TM59 reports are generated for each zone and avoids unnecessary outputs from being generated.

 

The "TM59 Lighting" Lighting template is also provided to allow appropriate lighting loads to be set, according to TM59 chapter 5.2. This can be selected on the Lighting tab.

Tip: The Load data from template tool can help speed up the Activity and Lighting template assignment process. See screenshot below.

 

  1. Open the Load data tab and choose the Activity to be applied.
  2. Open the Target tab and select all the relevant zones (be aware that when selecting Building or Block level, the inheritance process still works as usual).

 

 

An example of a fully assigned floor could look something like:

 

Tip: When naming a large number of zones, it can be helpful to use the Double-click to navigate site hierarchy Program option. This allows you to quickly and easily change the name of zones at Block level by clicking and editing the zone name in the Navigator without unnecessarily navigating to the Zone level. This leaves you ready to change the name of the next zone without having to navigate back up to block level

Internal Environment Control - Ventilation strategy

Choosing an appropriate ventilation strategy is an important part of the TM59 assessment process and therefore all the input data should be carefully selected and results should be analysed to assure that the window opening control works as designed.

 

When using the Calculated Natural Ventilation model option, the input is defined in the following sections of the Model data.

Activity Tab

HVAC Tab

Note 1: TM59 outputs will only be reported for zones without mechanical cooling.

Note 2: Natural ventilation must be activated on the HVAC tab before it is possible to access to the corresponding data for windows and vents on the Openings tab.

Implementation note

The TM59 standards states that:

“Windows in each room should be controlled separately and modelled as open when both the internal dry bulb temperature exceeds 22 °C and the room is occupied”.

To avoid windows opening when zones are not occupied and temperature is below 22° C, pre-defined TM59 Activity templates have Natural ventilation setpoint temperature set to 22° C and use default TM59 occupancy schedule.

 

Note that the 2-TemperatureControl mode provides idealised control in that when the outdoor air conditions are not favourable, openings are closed. i.e. openings are closed when Toutdoor > Tindoor to prevent introduction of warm air into the controlled zone. This may not be compliant with the TM59 standard because this type of an advanced control mechanism is not described in the standard which states simply that windows should be opened when Tindoor > 22° C and the room is occupied.

 

In summary TM59 requires that windows are open when the room is occupied and:

Tindoor > 22°C

Whereas the default DesignBuilder rule opens windows when:

Toutdoor < Tindoor > 22°C

Because the default DesignBuilder natural ventilation control rules do not comply exactly with the TM59 requirements, a 2-TM59 rules natural ventilation control override option is provided to guarantee that the openings stay open even when the outdoor conditions are not favourable. The TM59 natural ventilation rules override can be applied from the “Edit calculation Options” dialog > “Graphable outputs” > “Comfort and Environmental” > “CIBSE TM59” > “Natural ventilation rules”.

 

Note that by default, the override will be applied only to zones using TM59 Activity template (excluding corridors). Note also that the override only applies when using the Calculated natural ventilation model option.

Temperature control

Default TM59 activity temperature set points and schedules are based on the UK NCM data. Heating set point schedules have been modified to use heating setback temperature instead of set point in a period from May to September.

 

The environmental controls will typically be configured based on the building design.

 

To reduce the chance of simultaneous heating and window opening, a control mechanism is implemented through the Apply TM59 natural ventilation rules calculation option. See discussion above under HVAC tab.

Important note: The TM59 requirement to open the windows when the internal temperature rises above 22°C can easily lead to simultaneous heating and window opening. This is more likely to occur when:

- Heating setpoint temperature is close to the Ventilation setpoint temperature
- Large openable areas are present in the zone
- Lower “Time steps per hour” is used for simulation

In general, to avoid simultaneous heating and venting, the heating setpoint temperatures should not be greater than 21°C when modelling for TM59 overheating assessments.

Openings Tab

Note: Blinds and shading devices should be modelled according to TM59 chapter 3.7.

Internal openings

According to the TM59 standard:

“Internal doors can be included and left open in the model in the daytime, but should be assumed to be closed when the occupants are sleeping.”

To improve the flow of air through the airflow network, it will normally be beneficial to include internal openings such as doors, set to open based on the TM59 rules.

 

For any other details, guidance or restrictions regarding window and door opening refer to TM59 chapter 3.3.

Pipework, HIU and heat maintenance tape heat loss

Heat gains from pipework, heat interface units and heat maintenance tape, need to be manually added to relevant spaces using internal gains Activity model data. More information can be found in TM59 chapter 3.8.

Part-O Overheating Mitigation Calculations Building Regulations

The Approved Document O: Overheating, Section 2: Dynamic thermal modelling assessment is based on TM59, but with some limitations as explained below under Ventilation Rules.

Modelling Notes

SCHEDULE:COMPACT,

TM59_Studio_Occ_Restricted,

Fraction,

Through: 31 Dec,

For: WinterDesignDay,

Until: 24:00, 0,

For: AllOtherDays,

Until: 08:00, 0,

Until: 23:00, 1,

Until: 24:00, 0;

Running the TM59 Analysis

Calculation options - General

To obtain correct results it’s necessary to run a full annual analysis (1st Jan – 31st Dec). However, it is also important to run short term simulations, checking hourly / sub-hourly results to ensure that the ventilation / environmental control works as intended.

 

Bear in mind that the purpose of a TM59 analysis is to assess the risk of overheating and that because of the specific ventilation requirements of TM59, the same model might not generate accurate energy consumption results. To help avoid any such issues, the 1-Standard EnergyPlus controls option can be selected from the Natural ventilation rules calculation option drop list when running simulations where energy consumption is an important output.

Tip: Once you are happy that your model is running well and you are ready to generate TM59 results it is usually best to uncheck the hourly and sub-hourly output interval checkboxes on the Simulation Calculation options dialog to help keep result sets to manageable sizes.

Calculation options - Options

When using Calculated natural ventilation, you should generally use a simulation timestep of at least 6 timesteps per hour. While this will increase the simulation time it does provide more accurate results, especially for window opening control.

Calculation options - Simulation Manager

Using the Simulation Manager to run your TM59 simulations will enable you to continue working on the model while the simulation is running, and if necessary to run more than one simulation in parallel and compare the results side by side in the Results Viewer.

Note: To continue working in DesignBuilder or to run another simulation, the Simulation Manager dialog must first be closed.

Calculation options - Output

Results for the TM59 analysis can be obtained by selecting CIBSE TM59 output on the Output tab > Graphable Outputs. Other settings (Mechanical ventilation, vulnerable occupants) are discussed below.

 

Basic CIBSE TM59 output

Selecting the CIBSE TM59 output option will generate results according to the requirements of TM59 chapter 4.2 as described below.

 

 

To obtain results for Criteria 2 and 3 of CIBSE TM52 it is necessary to select TM52 outputs (results for TM52 and TM59 can be selected simultaneously).

 

By default, in TM59 calculations, the building category (based on CIBSE TM52 definitions) is Cat. II.

CIBSE TM59 Mechanical ventilation

 

DesignBuilder determines whether a building is predominantly mechanically ventilated through the settings on the HVAC tab and will add results according to TM59 chapter 4.3 as described below.

CIBSE TM59 Vulnerable Occupants

 

Selecting this output will change the building category for predominantly naturally ventilated buildings according to TM59 chapter 4.2 as described below.

CIBSE TM59 Corridors

 

Selecting this output will produce results according to TM59 chapter 4.5 as described below.

TM59:2017 Outputs

TM59:2017 results must be viewed in the DesignBuilder Results Viewer which can be accessed either from within DesignBuilder or from the Simulation Manager.

DesignBuilder Results Viewer

The Results Viewer is a separate application which can be used to view EnergyPlus results stored in one or more .eso files. It can be downloaded from the main Downloads > Software area of the DesignBuilder website. When installed, the application allows you to view any results contained within EnergyPlus .eso and .htm results files.

Standard Simulation (without Simulation Manager)

Results from the most recent simulation are stored in the eplusout.eso file in the EnergyPlus folder.

 

It is possible to use either of the following access routes implemented in the DB interface to open the file:

 

  1. Navigating to the EnergyPlus folder (File > Folders > EnergyPlus folder) and double-clicking on the eso file to open it in the Results Viewer.
  2. Using the toolbar icon on the Simulation screen.

 

 

Other ways to open .eso results files are:

 

Simulations using the Simulation Manager

The TM59 results can be accessed directly from the Simulation Manager interface by clicking on the View results in the DesignBuilder Results Viewer toolbar icon.

 

Understanding results displayed in Results Viewer

When you open an eso file in the Results Viewer that includes TM59 results, an extra CIBSE TM59 tab is displayed. Clicking on this tab reveals the summary TM59 results grid as shown below.

 

 

Criteria for homes predominantly ventilated

Compliance is based on passing both of the following two criteria:

 

(a) For living rooms, kitchens and bedrooms:

 

 

Criterion A is passed if the value is equal or less than 3%.

 

In the example output above Zone TypicalFlat:LivingRoomXKitchen fails to pass Criterion A because Hours of exceedance are greater than 3%.

 

(b) For bedrooms only:

 

 

Criterion B is passed if the value is equal or less than 32 hours.

 

In the above example both bedrooms pass Criterion B because the operative temperature is exceeded for less than 32 hours.

Criteria for home predominantly mechanically ventilated

All occupied rooms should not exceed an operative temperature of 26 ˚C for more than 3% of the annual occupied annual hours (CIBSE Guide A (2015a)).

Corridors: Assessment criteria

The overheating test for corridors should be based on the number of annual hours for which an operative temperature of 28 °C is exceeded. Whilst there is no mandatory target, if an operative temperature of 28 °C is exceeded for more than 3% of total annual hours, this should be flagged as a significant risk within the report.

In the above example both corridor zones pass the criteria with less than 3% exceedance.