Cooling

HVAC tab in model data - Simple HVAC

 

You can enter details on the cooling system including the maximum capacity (at zone level).

Note: for all systems, cooling setpoint temperatures are defined on the Activity tab.

Cooled

If the zone is to be actively cooled then check this checkbox. When it is checked the rest of the items described on this page become available.

Cooling capacity

The Cooling capacity can be entered manually when using Simple HVAC and when the HVAC sizing model option is set to either 2-Manual or 4-Autosize when not set.

 

This setting is not available when either of the 1-Adequate or 3- Autosize HVAC sizing model options are selected.

 

When 4-Autosize when not set is selected, if immediately prior to a Simulation the Cooling capacity is not set or it has a value of zero then a DesignBuilder Cooling design autosizing simulation is automatically run prior to the simulation to calculate it.

Tip: You can change cooling capacities by hand if you wish, but you should bear in mind that, when 4-Autosize when not set is selected, if the Model options or model geometry are changed, all heating and cooling capacities are reset to zero. You can set the HVAC sizing model option to 2-Manual to avoid losing your capacity settings due to model edits.

For more information about how this works, see HVAC sizing.

Supply Air Conditions

When using Simple HVAC  you can specify the cooling supply air conditions of the air.

Minimum supply air delivery temperature

The minimum dry-bulb air temperature of the air supplied for cooling the zone (in °C or °F).

Minimum supply air humidity ratio

The minimum humidity ratio (kg of water per kg of dry air) of the cool supply air. The default is 0.0077 kg-H2O/kg-air which corresponds to a 10C (50F) dew point. You should be careful to enter a value that is a valid condition, i.e. it is under the 100% saturation line on the Psychrometric Chart.

Cooling limit type

There are 3 ways that EnergyPlus ideal loads systems can limit zone cooling capacity (for simulations only):

 

Cooling Plant

Cooling fuel

Select the type of fuel used to generate the cooling energy - choose from:

 

Interface Fuel Name Fuel in results
1-Electricity from grid Electricity
2-Natural Gas Gas
3-Oil Oil
4-Coal Solid fuel
5-LPG Bottled gas
6-Biogas Bottled gas
7-Anthracite Solid fuel
8-Smokeless Fuel (inc Coke) Solid fuel
9-Dual Fuel Appliances (Mineral + Wood) Other
10-Biomass Other
11-Waste Heat Other

 

You should select 1-Electricity from grid you wish the results displayed in DesignBuilder to agree with those calculated by EnergyPlus directly for District cooling and displayed on the Summary tab of the Simulation screen.

Cooling system CoP

The cooling system coefficient of performance is used to calculate the fuel consumption required to meet cooling demand. The value represents the total seasonal efficiency of the entire cooling system and should include the effect of all energy consumption associated with building cooling such as fan and pump energy, chiller inefficiency, control equipment etc.

 

Cooling system CoP data is specified by zone so you can model different cooling efficiencies in each zone. But generally you should access this data from the building level and allow zones to take on building default.

Note: When comparing the cooling fuel consumption results with the data displayed on the Summary tab, it is important to realise that DesignBuilder applies a fuel type and a CoP to the idealised cooling systems used in EnergyPlus when using Simple HVAC. On the other hand EnergyPlus displays the unprocessed loads as District cooling in the tables on the Summary tab. This is because the idealised systems in EnergyPlus are considered to be met directly without use of HVAC equipment through a district cooling type system.

Operation

Cooling operation schedule

This schedule data is used in conjunction with the cooling setpoint temperatures on the Activity tab to define the time-varying cooling setpoint schedule in the zone. The operation schedule defines the times when full and setback setpoints should be met and the setpoint data on the Activity tab define the actual setpoint values. See Defining setpoint temperature schedules for more on this.

Note: the zone cooling operation schedule is also used in Detailed HVAC with the default 1-Simple HVAC Detailed HVAC Activity data setting.