HVAC tab in model data - Simple HVAC
The data required to define the heating system will depend on whether the HVAC model option is set to Simple or Detailed and if using Detailed the type of Detailed HVAC system selected.
Note: for all systems, heating setpoint temperatures are defined on the Activity tab.
If the zone is to be heated then check this checkbox. When it is checked the rest of the items described on this page become available.
The Heating capacity can be entered manually when using Simple HVAC and when the HVAC sizing model option is set to either 2-Manual or 4-Autosize when not set.
This setting is not available when either of the 1-Adequate or 3- Autosize HVAC sizing model options are selected.
When 4-Autosize when not set is selected, if immediately prior to a Simulation the Heating capacity is not set or it has a value of zero then a DesignBuilder Heating design autosizing simulation is automatically run prior to the simulation to calculate it.
Tip: You can change heating capacities by hand if you wish, but you should bear in mind that, when 4-Autosize when not set is selected, if the Model options or model geometry are changed, all heating and cooling capacities are reset to zero. You can set the HVAC sizing model option to 2-Manual to avoid losing your capacity settings due to model edits.
For more information about how this works, see HVAC sizing.
Select the type of fuel used to generate the heating energy - choose from:
| Interface Fuel Name | Fuel in results |
| 1-Electricity from grid | Electricity |
| 2-Natural Gas | Gas |
| 3-Oil | Oil |
| 4-Coal | Solid fuel |
| 5-LPG | Bottled gas |
| 6-Biogas | Bottled gas |
| 7-Anthracite | Solid fuel |
| 8-Smokeless Fuel (inc Coke) | Solid fuel |
| 9-Dual Fuel Appliances (Mineral + Wood) | Other |
| 10-Biomass | Other |
| 11-Waste Heat | Other |
You should select 1-Electricity from grid you wish the results displayed in DesignBuilder to agree with those calculated by EnergyPlus directly for District heating and displayed on the Summary tab of the Simulation screen.
The heating system Coefficient of Performance is used to calculate the fuel consumption required to meet heating demand. The value represents the total seasonal efficiency of the entire heating system and should include the effect of all energy consumption associated with building heating such as any boiler fan energy, boiler inefficiency, control equipment etc. It does not include energy involved in air or water distribution (fans or pumps) or control gear, which is accounted for in the Auxiliary energy.
Heating system CoP data is specified by zone so you can model different heating efficiencies in each zone. But generally you should access this data from the building level and allow zones to take on building default.
Note: When comparing the heating fuel consumption results with the data displayed on the Summary tab, it is important to realise that DesignBuilder applies a fuel type and a CoP to the idealised heating systems used in EnergyPlus when using Simple HVAC. On the other hand EnergyPlus displays the unprocessed loads as District heating in the tables on the Summary tab. This is because the idealised systems in EnergyPlus are considered to be met directly without use of HVAC equipment through a district heating type system.
There are two heating types available:
When using Simple HVAC you can specify the heating supply air conditions of the air.
The maximum dry-bulb air temperature of the air supplied for heating the zone (in °C or °F).
The constant humidity ratio (mass of water per mass of dry air) of the warm supply air to be delivered when heating is required. The default humidity ratio is 0.0156. You should be careful to enter a value that is a valid condition, i.e. it is under the 100% saturation line on the Psychrometric Chart.
There are 3 ways that EnergyPlus ideal loads systems can limit zone heating capacity:
Technical description
EnergyPlus uses the following 4 settings to define the maximum heating input for ideal loads systems:
Maximum Heating Supply Air Temperature
Maximum Heating Air Flow Rate,
Maximum Sensible Heating Capacity
Heating Limit Type
When using the default 3-Autosize HVAC sizing Model option the "Maximum Heating Supply Air Temperature" and "Heating Limit Type" IDF fields are set using corresponding data from the HVAC tab, and the "Maximum Heating Air Flow Rate" and "Maximum Sensible Heating Capacity" fields are calculated by EnergyPlus before the simulation in the design sizing calculations.
Alternatively, when using either of the 2-Manual or 4-Autosize when not set HVAC sizing Model options, the "Maximum Heating Supply Air Temperature", "Maximum Sensible Heating Capacity" and "Heating Limit Type" IDF fields are set using corresponding data from the HVAC tab, and DesignBuilder calculates the corresponding "Maximum Heating Air Flow Rate" based on the user-defined Heating capacity and Maximum supply air delivery temperature data. In this case all of the 4 related IDF fields are specified in the IDF by DesignBuilder.
Or when the 1-Adequate HVAC sizing Model option is selected, DesignBuilder sets the EnergyPlus "Heating Limit Type" IDF field to "NoLimit" which means that the heating system can meet any load. In this case the other 3 fields are not needed and so are not provided in the IDF.
In all of the above cases, apart from when the 1-Adequate HVAC sizing Model option is selected, EnergyPlus holds values for each of the 4 settings used to define the maximum heating input for ideal loads systems, and the way these are used in the simulation is defined by the Heating limit type per the above descriptions.
Note: In practice this setting should not make a noticeable difference to the thermal heat balance of the zone during heating since the maximum heat delivery to the zone is already defined before the simulation and this setting simply tells EnergyPlus exactly how to apply the limit.
When the Simple HVAC, 1-Room ventilation Mechanical ventilation and 1-DesignBuilder Simple HVAC autosizing method model options are set you can model radiant heating systems. Set the heating system type as 2-Radiant/convective units (above) and enter the heating radiant fraction and the way radiant heat is distributed through the space.
Important: Recent versions of EnergyPlus no longer support the radiant/convective option combined with Simple HVAC cooling systems, so if you need radiant heating and cooling in the same zone then you should switch to Detailed HVAC.
The fraction of the power input to the radiant heater that is actually radiant heat transfer. The fraction should be between 0 and 1. In conjunction with the Radiant distribution option, it defines the breakdown of how the power input to the heater is distributed to the rest of the zone.
The Radiant distribution allows you to control how the radiant heat from the Radiant unit is distributed around the room. Options are:
Technical Note
DesignBuilder uses the EnergyPlus 'HIGH TEMP RADIANT SYSTEM' to model radiant heating systems when in Simple HVAC mode. This system type is intended for modelling 'high-temperature' radiant sources but it can equally well be used for low temperature radiant sources.
Note: for all Simple HVAC systems, heating setpoint temperatures are defined on the Activity tab.
By default EnergyPlus does not account for mechanical and natural ventilation (outdoor air) loads in Heating design calculations so the options below are provided to add an extra load for Winter design day only.
Define how mechanical ventilation loads should be dealt with in Heating design calculations. Options are:
Note: The default Mechanical ventilation load setting is 1-Met by zone equipment. For DOAS systems which introduce air that is partially or fully pre-heated, this setting should be changed to 2-Exclude or to 3-Partially met by AHU to ensure that zone equipment is not oversized.
Note: This setting applies only to Heating design calculations. For Detailed HVAC simulations the DOAS settings on the HVAC zone group dialog are used instead to account for any additional loads due to mechanically supplied fresh air. For Simple HVAC the full outdoor air load is assumed when sizing heating and cooling systems, no preheat/precool is assumed when sizing zone equipment.
When Mechanical ventilation load is set to 3-Partially met by AHU then you must enter the supply air temperature to enable the residual additional zone loads required to be accounted for.
If the savings provided by heat recovery can be safely included in the heating sizing calculations then leave this checkbox unchecked. Otherwise for a safer calculation where zone heating systems are sized based on no heat recovery being available then check this option.
If natural ventilation is activated then you can define how natural ventilation loads should be dealt with in Heating design and simulation autosizing simulations. Options are:
This schedule data is used in conjunction with the heating setpoint temperatures on the Activity tab to define the time-varying heating setpoint schedule in the zone. The operation schedule defines the times when full and setback setpoints should be met and the setpoint data on the Activity tab define the actual setpoint values. See Defining setpoint temperature schedules for more on this.
Note: the zone heating operation schedule is also used in Detailed HVAC with the default 1-Simple HVAC Detailed HVAC Activity data setting.